what is the function of anti-pumping in circuit breaker?
Answers were Sorted based on User's Feedback
Answer / amit kr jha
The anti-pumping relay is a device in circuit-breaker whose function is to prevent multiple breaker closures. For instance, if the operator gives the closing command to the breaker by pressing the close button and the breaker closes. However, a fault in the system causes the breaker to trip. Since the close command is still in the pressed condition, there is a chance of the breaker closing again and being tripped by the relay multiple times. This can damage the closing mechanism of the breaker. The anti-pumping relay prevents this by ensuring that the breaker closes only once for one close command from the control panel
| Is This Answer Correct ? | 4 Yes | 0 No |
Anti-pumping function. After fault tripping or intentional
opening using the manual or electrical controls, the closing
order must first be discontinued, then reactivated to close the circuit breaker.
From Schneider Electric Catalogue
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ravi kumar dontha
Simply say Anti pumping relay will bypass the closing coil
from DC input supply if we keep on giving input to the coil
through TNC switch for more than one cycle(1/50=20msec).
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / arati lahoti
When breaker is in closed condition at that time Anti-pumping prevents the reclosing of breaker. In short it does not allow to give again the closing command to breaker.
| Is This Answer Correct ? | 1 Yes | 0 No |
The Anti pumping relay is provided with closing circuit of
Circuit Breaker, which prevents the repetitive closing
Command to the breaker. Actually closing coils are not designed for continuous operations, if you give constant commands this coil may
burnt. So to prevent this antipumping contactors are used.
Therefore anti-pumping coil used to by pass the repetitive closing command.It is used to save the closing coil.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / bibin jose
Anti-pumping device is a feature incorporated in a Circuit Breaker or reclosing scheme to prevent repeated operation where the closing impulse lasts longer than the sum of the relay and CB operating times. The function of an anti-pumping device is to prevent the circuit breaker closing and opening several times in quick succession. This might be caused by the application of a closing pulse while the circuit breaker is being tripped via the protection relays. Alternatively, it may occur if the circuit breaker is closed on to a fault and the closing pulse is longer than the sum of protection relay and circuit breaker operating times. Circuit breakers with trip free mechanisms do not require this feature.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / veeresh k
It block the closing pulse when breaker is already closed condition
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vipul
as we discussed earlier,anti puming relay avoids the
multiple clossing of the breaker,if we press the close
button while the breaker is already closed,anti puming
relay comes into action.ano contact of the anti pumping
relay is connected parallely to the close coil of the
breaker.if we go on pressing the close button, parallely
connected coil will energise not close coil
| Is This Answer Correct ? | 0 Yes | 2 No |
In ckt bkr closing coils are not designed for continous
operations, if you give constant commands this coil may
burnt. so to prevent this antipumping contactors used in CC
ckt.
| Is This Answer Correct ? | 23 Yes | 33 No |
The contacts of this relay prevent uncontrolled discharging
of the closing spring, if the closing signal remains
complete up to the breaker. If the circuit remains
complete, the closing spring would discharge under the
wrong conditions, this is called pumping.
| Is This Answer Correct ? | 6 Yes | 24 No |
What is Difference Between Induction Motor & Servo Motor
31 Answers Jindal, Kirloskar, KTTM, Star Technocrates, Toyota,
how can maintaince the acb contactor moveing and fixing kit
is there any concept of armature reaction in Induction motor?
why diesel tank is earthed
When neutral is grounded in electrical circuit?
Details about Flux Compensated magnetic Amplifer starter for motors
What is MSL designation of a motor and same may be provided in details.
How it can worked plc based electrical system And which type of software using.
1 Ton is equal to how many watts?
Why two nos. un-tensioned wires are placed inside the PSC poles used by powergrid in RGGVY works.
Is it possible to obtain 480v or 550v in single phase output by giving the input to 230v to a single phase torodial type transformer without using a stepup transformer?
how to make a solar panel? why solar panel cell connected to serious?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)