what is the function of anti-pumping in circuit breaker?
Answer Posted / kayode j.
The anti-pumping relay is a device in circuit-breaker whose
function is to prevent multiple breaker closures. For
instance, if the operator gives the closing command to the
breaker by pressing the close button and the breaker
closes. However, a fault in the system causes the breaker
to trip. Since the close command is still in the pressed
condition, there is a chance of the breaker closing again
and being tripped by the relay multiple times. This can
damage the closing mechanism of the breaker. The anti-
pumping relay prevents this by ensuring that the breaker
closes only once for one close command from the control
panel.
| Is This Answer Correct ? | 249 Yes | 12 No |
Post New Answer View All Answers
what causes contact chatter when there is no demand on the air conditioning unit?
please describe the Transformer setting, Motor setting, I/C setting, Tie setting
What is the meaning of Insulation H for transformers????
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
What is acsr cable and where we use it?
1.why we are using metal oxide gapless block in lightning arrester,2.What is minimum and maximum rating of metal oxide blocks using in india
determine two methods to find loose connection in operational electrical system?
we have amp, voltage, kw, length detail then how to calculte copper & alluminium size of conductor of 3-phase induction motor
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
What is difference between start imitation and start interlock for 3 phase motor protection ?
Help need in transformer !? Hello Friends The parameters of 2300/230 v 50hz t/f is R1=0.286 ohm R`2=0.319 ohm Rc=240 ohm X1=0.73 ohm X`2=0.73 ohm Xm=49.2 ohm Secondary Load impedance ZL=0.387+J0.29 solve the exact equivalent circuit with normal voltage across primery.. I know every thing but i cant find CURRENT I1=? and I`2=? Please help me give solution or only Formula please please...
what is the differation bewreen kwh & fundamental kwh in electronic trivector meters
What is the count of hvdc transmission lines in india?
I WANT BHEL PREVIOUS QUESTION
What is the basic of DTH.