how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?
Answers were Sorted based on User's Feedback
Answer / prashant soni
HT Cable size dependson fault level to be withstood and its duration..
If you take XLPE, HT Cable of ALU conductor,
condiering 350MVA for 1 sec *(18.37kA), min. C/A will be found out by Area(A) = (Short ckt current (kA)*Square root of Time)/k
k is constant = 0.094 for XLPE ALu conductor.
This will give you min. size required for HT system (11/22/33/6.6/3.3kV)
Choose nearest standard higher size for HT Cable..
primary 3*240 sqmm AL cable
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ahmed
how many cable shoul be connected for 2000kva transformer of 11kv.
primary 3*240 sqmm AL cable
Secondry 4*630 sqmm AL / single phase (L1,L2,L3 & L4)
(u1,u2,u3 & u4) R-Phase
(v1,v2,v3 & v4) Y-Phase
(w1,w2,w3 & w4) B-Phase
(N1,N2,N3 & N4) Neutral
Is This Answer Correct ? | 2 Yes | 2 No |
Simultaneous trip of incoming and outgoing breakers of 400kv/220kv trnasformer. What are the probable causes?
what is frequency transformer?
What is disc insulator and it's application..?
How can you limit the fault level in a power system?
11 KV Power cable end earth connection insulation got burned wht is the reson pl give the resons
what is current actully?significance of current...not rate of change of flow.....
How many companies are manufacturing 33 KV HT Breaker
how is choose &depending upon the load why?
It is advisable 2 use auto-transformer if transformation ratio is-a)110KV/11KV,b)230kv/110kv,c)110kv/66kv,d) 400kv/230kv
WHAT IS MEANING OF Gg & Gg IN hrc FUSE
what will happen if ac and dc supplies given
will we get shock from dc?