Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?

Answers were Sorted based on User's Feedback



how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?..

Answer / prashant soni

HT Cable size dependson fault level to be withstood and its duration..

If you take XLPE, HT Cable of ALU conductor,
condiering 350MVA for 1 sec *(18.37kA), min. C/A will be found out by Area(A) = (Short ckt current (kA)*Square root of Time)/k
k is constant = 0.094 for XLPE ALu conductor.

This will give you min. size required for HT system (11/22/33/6.6/3.3kV)

Choose nearest standard higher size for HT Cable..
primary 3*240 sqmm AL cable

Is This Answer Correct ?    2 Yes 0 No

how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?..

Answer / ahmed

how many cable shoul be connected for 2000kva transformer of 11kv.

primary 3*240 sqmm AL cable


Secondry 4*630 sqmm AL / single phase (L1,L2,L3 & L4)
(u1,u2,u3 & u4) R-Phase
(v1,v2,v3 & v4) Y-Phase
(w1,w2,w3 & w4) B-Phase

(N1,N2,N3 & N4) Neutral

Is This Answer Correct ?    2 Yes 2 No

how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?..

Answer / upen

250sqmm

Is This Answer Correct ?    2 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

why are we using resistor in NGR ?

1 Answers  


i have DEEE certificate in vinyaka misson unive rsity. is a INGNO if possible get the electrical C licences in Tamil nadu?

0 Answers  


what are the insulation properties.

2 Answers   Cable Wireless, MAHINDRA,


what curve and rateing would you use for a three phase 0.75kw motor?

0 Answers  


what is the calculation formula for motor starting torque,running torque, running torque.

0 Answers  


What is the function of PMG in DG sets & how it works??????????

2 Answers  


what is bus coupler? and how many type? which one is big advantage ?

2 Answers   Essar,


I have been short listed for sydicate clerkcal post .i have interview on 15th sept..i want to ask if i don't know kannada to read and write they won't allow me to attend the interview?Do send u r reply.......

1 Answers   Syndicate Bank,


how to calculate cable size in diffrent loads?

0 Answers   ABB, Sterling,


Going in for a three phase motor or a single phase motor, what factor should be considered for this? For eg., to pump water to certain height and such domestic applications, which motor is suitable?

1 Answers  


Why 11KV PT Secondaries [(11000/1.732)/(110/1.732)/ (110 / 3)]are in star connection ? And why the same should not be in delta ?

1 Answers  


I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.

9 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)