how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?
Answers were Sorted based on User's Feedback
Answer / prashant soni
HT Cable size dependson fault level to be withstood and its duration..
If you take XLPE, HT Cable of ALU conductor,
condiering 350MVA for 1 sec *(18.37kA), min. C/A will be found out by Area(A) = (Short ckt current (kA)*Square root of Time)/k
k is constant = 0.094 for XLPE ALu conductor.
This will give you min. size required for HT system (11/22/33/6.6/3.3kV)
Choose nearest standard higher size for HT Cable..
primary 3*240 sqmm AL cable
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ahmed
how many cable shoul be connected for 2000kva transformer of 11kv.
primary 3*240 sqmm AL cable
Secondry 4*630 sqmm AL / single phase (L1,L2,L3 & L4)
(u1,u2,u3 & u4) R-Phase
(v1,v2,v3 & v4) Y-Phase
(w1,w2,w3 & w4) B-Phase
(N1,N2,N3 & N4) Neutral
| Is This Answer Correct ? | 2 Yes | 2 No |
why are we using resistor in NGR ?
i have DEEE certificate in vinyaka misson unive rsity. is a INGNO if possible get the electrical C licences in Tamil nadu?
what are the insulation properties.
2 Answers Cable Wireless, MAHINDRA,
what curve and rateing would you use for a three phase 0.75kw motor?
what is the calculation formula for motor starting torque,running torque, running torque.
What is the function of PMG in DG sets & how it works??????????
what is bus coupler? and how many type? which one is big advantage ?
I have been short listed for sydicate clerkcal post .i have interview on 15th sept..i want to ask if i don't know kannada to read and write they won't allow me to attend the interview?Do send u r reply.......
how to calculate cable size in diffrent loads?
Going in for a three phase motor or a single phase motor, what factor should be considered for this? For eg., to pump water to certain height and such domestic applications, which motor is suitable?
Why 11KV PT Secondaries [(11000/1.732)/(110/1.732)/ (110 / 3)]are in star connection ? And why the same should not be in delta ?
I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)