Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is diffrential relay used in generator
plz give brief explanation

Answers were Sorted based on User's Feedback



what is diffrential relay used in generator plz give brief explanation..

Answer / suresh

diffrential relay used in generator for sense the winding
fualt

Is This Answer Correct ?    2 Yes 0 No

what is diffrential relay used in generator plz give brief explanation..

Answer / saad

That works on difference of two current thats why known as
diffrential relay for example two cts one on generator
phase ct and other r on neutral side both cts passing for
example 5amps but the direction of current iz opposite so
the resultant iz zero that senses the relay if there is any
fault in the generator so the current increase on fault
side and the dirrence current increase and relay trip the
CB that iz the protection of generator transformer winding

Is This Answer Correct ?    0 Yes 0 No

what is diffrential relay used in generator plz give brief explanation..

Answer / musa

diffrential relay main protection for generator and
transformer ,between protection area not for outage short
circuit

Is This Answer Correct ?    1 Yes 3 No

what is diffrential relay used in generator plz give brief explanation..

Answer / ashish umrao

the diffrential relay used in which position when proctect
the specfice jone like feeder ,tranfromer ,bus bar,has a not
fluctuate the voltage .but generator has a variable load so
voltage are up and down so dose not use the this relay.

Is This Answer Correct ?    1 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

What is P.F? Formula for calculating PF in HT side?

1 Answers  


what is diff. between earthing grid,earthing mess, earting grid?

0 Answers   Century Rayon, Emco, Tailor Solution,


difference between cable and conductor?

6 Answers   TransOcean,


If any HVDC line is going with positive & negative(the negative usually have return path of current with earthing electrode). Now the question is if this HVDC earthed electrode which is using as return path and earthed any nearby 400kv or 220kv AC substation equipments. which will be the impact of this on AC substation & its equipment, how severe may be this and what should be the minimum distance require between HVDC earthed electrode and AC substation equipments? It's really an high engineering level question...Dare to answer and increase your knowledge.

0 Answers   MEIL,


Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.

0 Answers   Piramal Healthcare,


Where the Dry type tranformers are used.

5 Answers  


Basic philosophy of applying 3P tripping for uptill 132KV switchyards & for 132KV & above 1P/3P tripping is used.

1 Answers   L&T,


What is the formula for calculating transformer Efficiency?

2 Answers  


is 60hz freq better than 50 hz?&why?

1 Answers  


Comparative difference between 33Kv & 66KV for transmitting the load of 7 MW at a distance of 34 Km.

6 Answers   NHPC,


why t/f are rated in kva. is it conserned with p.f.

3 Answers  


How to calulate cable size for 200KVA,160KVA& 40KVA load?

1 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)