In HT overhead line why should provide top conducter which
is not connected whith insulater..?
Answers were Sorted based on User's Feedback
The top one is the earthing conductor. It is used to
protect the lines from the "LIGHTINGS".
| Is This Answer Correct ? | 28 Yes | 4 No |
Answer / kaushik ( ms university)
The wire provided at top of the tower to tower is a ground
wire.it is used for protection against LIGHTNING STROKE. &
it is grounded at regular interval of tower.
| Is This Answer Correct ? | 5 Yes | 0 No |
What is non-minimum phase transfer function?
how can a transformer test by megger?
how we can select MCB ratings according to Voltages, Curves.
what are the settings is there for ABB REM543 Generator Protection Relay
Why current flows in nutral? As per theory there should be no current in 3 ph explain.
How to calculate fault level of 11 KV system
what is Ith current?
What do you mean by per capita requirement of electrical energy in india
What is the minimum load that you can keep in a 3 Phase 40 KVA Diesel Generator? Is it neccessary to load all the 3 phases? Can a phase be left without load?
it is possible to run 130V AC and 230 V AC cables run in same tray
In generally how many earthing required for power
what is the internal working of star delta starter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)