Befor synchronissation of Generator what test to be carried
out.pl.specify with reason.
Answers were Sorted based on User's Feedback
Answer / vijay
Before Synchronisation mainly three conditions
(voltage,speed/frequency & Phase sequence) has to be
checked which are within the limits. Reason to monitor when
any one on this parameters found not in unique, DG set's
not getting synchronised.
If the synchronisation happened in unconditional status, it
causes unbalance current will flow in the operation and
load sharring is not even. To eliminate this kinds of
occurence Dark lamp test was carried out before execution.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer one is mostly correct. Two other factors are important. 1) the winding type (e.g. 2/3 or 5/8) as this can affect circulating neutral current. 2) phase angle at time of synchronising must be within limits to prevent high currents to pull DGs into synch.
For answer two - load sharing equipment can allow DGs of different ratings to be used in parallel. Frequency is important not RPM. The number of poles in an alternator can vary requiring a different RPM for the same frequency.
Another important factor iis governor response to load changes
| Is This Answer Correct ? | 0 Yes | 0 No |
BOATH THE DG'S ARE EQUAL RATING(KVA)
BEFORE SYNCHRONISING THE TWO DG'S TO CHECK 1)BUS VOLTAGE
2) FREQUENCY 3) RPM
| Is This Answer Correct ? | 0 Yes | 4 No |
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
why do we have 230v a.c. as general voltage for domestic supply rather than others?
How we find the size of cable if we know the current
Plz tell me how we can find that particular company has vacancy or not
where rlc series ckt used?
howmuch current can carry the 2.5Sqmm copper cable?
what is use of capacitor in fan
how could we know the size of cable by physical view?
0 Answers Havells, United Engineering,
what is the relation between knowing of the distance between power transformer and the capacitor feeder in case of parallel operation
why is a earth pit 10 ft usually? And, what should be the distance betweeen two earth pit?
why designer use kva rating instead of kw in transformer rating???????????????
What is the types of HT motor testing
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)