why designer use kva rating instead of kw in transformer rating???????????????..

Answer / minal

Transformer are always rated in Kva because there are 2
losses in transformer.
one is copper loss which depends on current & the other is
iron loss which depends on voltage & not affected bypower
factor.
Thus transformer rating in kva & not in kw.

Is This Answer Correct ?    104 Yes 10 No

why designer use kva rating instead of kw in transformer rating???????????????..

Answer / md. jafar iqbal

The total losses of a Transformer= Core loss+Copper loss.
Core loss depends on voltage and copper loss depends on
current that means total losses depends on current & volage
but not depends on their phase angle.There is no relation
between the total loss of a transformer and the change of
power factor. This is why rating of a transformer is
written KVA not KW.

Is This Answer Correct ?    34 Yes 7 No

why designer use kva rating instead of kw in transformer rating???????????????..

Answer / integratorman

Transformer losses are related to the efficiency of the
transformer. The Power factor of a transformer depends on
the load attached to it. if that load is resistive, power
factor is usually considered 1, in which case KVA = kW. if
the load is inductive or capacitive, then power factor
should be taken into consideration when sizing the
transformer.
Hence the transformer is designed for voltage and current
output(VA) - how you apply the transformer determines how
many watts there is in the circuit.

Is This Answer Correct ?    23 Yes 3 No

why designer use kva rating instead of kw in transformer rating???????????????..

Answer / amolkarne

x'mers,UPS,DG etc are rated in KVA beacause at the time of
manufacturing manufacturer is unknown about the type of
load (inductive,capacitive or resistive)that perticular m\c
is going to suypply.so there is no question of pf to be
considerd to give it's rating in KW...........
KVA = KV X Amps -(1)
KW = KV X Amps X P.F. -(2)

it gets more clear by looking towards above formulae

Is This Answer Correct ?    21 Yes 6 No

why designer use kva rating instead of kw in transformer rating???????????????..

Answer / blake

The KVA rating of a transformer takes into account the
power factor of the supply system. i.e. If you have a 100kW
load on your system with a supply power factor of 0.8 then
your transformer will need to be at least 125kVA. p.f =
KW/KVA. So to answer the question a KVA rating allows for
the fact that differnt installations can have different
power factors.

Is This Answer Correct ?    40 Yes 31 No

why designer use kva rating instead of kw in transformer rating???????????????..

Answer / ramesh kumar k

All answers explains two different reasons for this..
Both are correct...Mr. Integratorman's answer gives good
explanation for Mr. Blake's answer.. This reason is not
explained in many text books.. These two people are also
right... along with others..

Is This Answer Correct ?    6 Yes 1 No

why designer use kva rating instead of kw in transformer rating???????????????..

Answer / nibel

transformers are rated in kva coz we cant judge the type of
load(either inductive or capacitive) used by us. so we cant
find the power factor on the load side. finally no one use
kw only kva, (Kw=kva*pf)

Is This Answer Correct ?    0 Yes 0 No

why designer use kva rating instead of kw in transformer rating???????????????..

Answer / devi

Transformer rating written in always kva because depends
upon the voltage and current rating.

Is This Answer Correct ?    16 Yes 17 No

why designer use kva rating instead of kw in transformer rating???????????????..

Answer / rudra

kVA is the unit for apparent power. Apparent power consists of active and reactive power. Active power is the share of the apparent power which transmits energy from the source to the user. Reactive power is the share of the apparent power which represents a useless oscillation of energy from the source to the user and back again.

This means that the current does not change polarity synchronous with the voltage. But the heat generated in a winding as well as the eddy current losses generated in a transformer core depend on the current only, Therefore the heat is always proportional to the square of the current amplitude, irrespective of the phase angle. So a transformer has to be rated by apparent power.

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what is the similarity and difference between ups and inverter?

4 Answers   GMR,


why does rotor rotets?

0 Answers   IBM,


WHAT IS THE DIFFERENCE B/WDYNAMO&ALTERNATOR?

6 Answers   IOCL,


Sir, I completed DEEE... And now I working in TNEB for one year apprenticeship. If I eligible for applying c license and how can I get?

1 Answers  


Differentiate between induced emf and self inductance?

0 Answers  






What is the black star?

2 Answers  


How to Calculate IKW(input kilowatt)of a Chiller plant

2 Answers   Voltas,


what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV

0 Answers  


What is High Frequency Grounding????

2 Answers   Emerson,


what is the IPC ? & what the uses ?

0 Answers   Bhel,


HOW many type of Circut Breaker in the world used in 400 kv substation?

14 Answers   Power Grid,


WHAT R THE SAFETIES IN A HIGH TENSION PANEL N LOW TENSION PANEL. ALSO WAT SAFETIES R THERE IN A 200 KVA TRANSFORMER?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)