Answer / minal
Transformer are always rated in Kva because there are 2
losses in transformer.
one is copper loss which depends on current & the other is
iron loss which depends on voltage & not affected bypower
factor.
Thus transformer rating in kva & not in kw.
| Is This Answer Correct ? | 104 Yes | 10 No |
Answer / md. jafar iqbal
The total losses of a Transformer= Core loss+Copper loss.
Core loss depends on voltage and copper loss depends on
current that means total losses depends on current & volage
but not depends on their phase angle.There is no relation
between the total loss of a transformer and the change of
power factor. This is why rating of a transformer is
written KVA not KW.
| Is This Answer Correct ? | 34 Yes | 7 No |
Answer / integratorman
Transformer losses are related to the efficiency of the
transformer. The Power factor of a transformer depends on
the load attached to it. if that load is resistive, power
factor is usually considered 1, in which case KVA = kW. if
the load is inductive or capacitive, then power factor
should be taken into consideration when sizing the
transformer.
Hence the transformer is designed for voltage and current
output(VA) - how you apply the transformer determines how
many watts there is in the circuit.
| Is This Answer Correct ? | 23 Yes | 3 No |
x'mers,UPS,DG etc are rated in KVA beacause at the time of
manufacturing manufacturer is unknown about the type of
load (inductive,capacitive or resistive)that perticular m\c
is going to suypply.so there is no question of pf to be
considerd to give it's rating in KW...........
KVA = KV X Amps -(1)
KW = KV X Amps X P.F. -(2)
it gets more clear by looking towards above formulae
| Is This Answer Correct ? | 21 Yes | 6 No |
Answer / blake
The KVA rating of a transformer takes into account the
power factor of the supply system. i.e. If you have a 100kW
load on your system with a supply power factor of 0.8 then
your transformer will need to be at least 125kVA. p.f =
KW/KVA. So to answer the question a KVA rating allows for
the fact that differnt installations can have different
power factors.
| Is This Answer Correct ? | 40 Yes | 31 No |
Answer / ramesh kumar k
All answers explains two different reasons for this..
Both are correct...Mr. Integratorman's answer gives good
explanation for Mr. Blake's answer.. This reason is not
explained in many text books.. These two people are also
right... along with others..
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / nibel
transformers are rated in kva coz we cant judge the type of
load(either inductive or capacitive) used by us. so we cant
find the power factor on the load side. finally no one use
kw only kva, (Kw=kva*pf)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / devi
Transformer rating written in always kva because depends
upon the voltage and current rating.
| Is This Answer Correct ? | 16 Yes | 17 No |
Answer / rudra
kVA is the unit for apparent power. Apparent power consists of active and reactive power. Active power is the share of the apparent power which transmits energy from the source to the user. Reactive power is the share of the apparent power which represents a useless oscillation of energy from the source to the user and back again.
This means that the current does not change polarity synchronous with the voltage. But the heat generated in a winding as well as the eddy current losses generated in a transformer core depend on the current only, Therefore the heat is always proportional to the square of the current amplitude, irrespective of the phase angle. So a transformer has to be rated by apparent power.
| Is This Answer Correct ? | 1 Yes | 3 No |
what is x'mer ,isolation x'mer & yltra-isolation x'mer?????
Why ground terminal is used in pot meter 10k ohms
What types of question are done for diploma students in aptitude test
How much ph is maintained of water electrolyte which is used in LRS for 1200 kw slipring induction motor ?
0 Answers AMS, JK Lakshmi Cement,
Why we use auxillary relay ? what is function of differential relay, directional o/c relay?
0 Answers Century Rayon, Mechanical,
Why is it that polarization index type test is required for MV and HV motors and not for LV motors?
3 Answers La-Gajjar Machineries, Qatar Airlines,
Why ferranti effect occurred in leading p.f load?
List some examples of renewable energy?
In track electrification Either we use single conductor or double conductor? why?
what is the power factor of choke coil used in tubelight
how to set time from star to delta starter
Q-1 what are the structural and operational difference between a distribution and a power transformer? Q-2 what is skew in motors? Q-3 draw equivalent circuit of transformer Q-4 explain with phasors how pf is improved with loading in induction motors Q-5 DIFFERENT METHODS OF CABLE LAYING(interviewer asked if i heard new chemical based earthing system next) Q-6 pi model of medium length trans line Q-7 v/f control?why Q-8 vacuum circuit breaker operates in?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)