why use delta star x-mer in distribution system.
Answers were Sorted based on User's Feedback
Answer / blake_australia
The star point on the secondary site of the transformer
provides an earth return point for earth faults. The
previous answer is also correct.
Also 3rd Harmonics are circulated within the primary delta
winding which prevents the LV harmonic distortions from
entering the Primary side of the distribution network.
| Is This Answer Correct ? | 23 Yes | 4 No |
Answer / rabi
In distribution system, required voltage level is mainly
220V which can be obtained with star connected secondary
(415/√3) as there is a provision of neutral. Also the
insulation coast for the secondary will be less the voltage
level is less in secondary.
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / b s patil
The used of(Delta/star) step dowen transformer in
distribution system for single phase power supply and
control supply means used of neutral for single phase.
| Is This Answer Correct ? | 4 Yes | 1 No |
what is relation of rpm with Power supply? rpm directly Proposational to power ?
How much weight an electrical engine can pull??
Why did lightening arrestor solid copper rod head is sharp on mobile tower top?
what is the significance of per unit impedance ?
can we transmit power with out cable if it is possible how it is possible.
What is the difference between a Distribution Transformer and a Power Transformer.
What is the difference between PLC and Embeded system
what happens when a DC supply is given to AC motor?
why do we require two lines one phase and a neutral for an ac transmission..is neutral potential zero..?if yes y carry a neutral line from generating station itself...why dont we take it from ground
What is distance protection relay? where & why we use this relay?
2 Answers Siemens, UltraTech, Voltech,
when meggering a 3ph,480v oil reservoir heater on a regen gas compressor, why do I get a reading to ground when meggering phase to ground? shouldn't it read opened or is there something that makes it read closed? on the same heater, when ohming, it reads open. thanx
A 3PH MOTOR RUNNING IN NORMAL CONDITION AND ITS AMPERE ALSO UNDER ITS FULL LOAD CURRENT,ITS CABLE RATINGS ALSO HIGER THN ITS CAPACITY,BUT ITS CABLE GETTING ABNORMAL HEAT(NOT TOO HOT)WHY ITS GETTING HOT LIK THIS
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)