why rating of generator is kva but motor is kw ?
Answers were Sorted based on User's Feedback
Answer / jahangir
Transformer and genrator PF depends on the nature of
connected load ( Motor ), But motor has its own fixed Power
factor
Therefore Transformer and genrator capacity shown in KVA (
Without PF ) and motor Capacity shows in Kw ( with power
factor )
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / gunnam santosh
kw=kva*pf
powerfactor depends on loads, transformers and generators
are not designed for a specific loads,the powerfactor of
these tf and gen are know by knowing the powerfactor of the
load which is being supplied by them.so their ratings are
given in kva
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arun kumar.k
Generator is produsing the power supply and it is flow of
electron it in form of VA
AND they have own rating and they have own power factor
In motor we calculating the efficiency
>efficiency it always in watts or workdone
>And WE cant relate kva to the load
LOad it s only carry the kw Because load only utilizing
the power and we want to exepcet the load only efficiency
or Work done
>load is only for power utilizing
Is This Answer Correct ? | 0 Yes | 0 No |
I want to wire sizing calculator which website is available it
what's the difference between 'shaft power demand' and 'BHP' , when we consider electrical load list.
Explain Creepage Distance of Insulator
How the setting of the vector surge relay shall be calculated when the relay is to be used for Grid islanding application?
Difference between transmission line and cable?when ever a large water channel has to crossed it is easier to use cable then transmission line why?
which generator is called as brushless excitation generator and why??
can we apply kirchhoff's laws to circuits containing non linear elements?
in pf lagging means current decrease by increasing voltage is correct or not ? reason ?
what is the write prosidure of stringing of 8meter pcc pole.
What are the protection used for alternator,transformers.
what will happen if ac power supply is given to the rotor of an alternator
An AC coil to give DC supply whats happen in the coil.what type of problem are create.