hi vishok this is noor plz tell me what type problems will
occured i use T/C in the place of RTD in (FEED WATER
TANK),plz send ur e-mail address to my ID
(mail2noor.hyd@gmail.com)
Answers were Sorted based on User's Feedback
Answer / bm
No problem will occur if you use T/C inplace of RTD.
However as the temperature in feed water tank is less, and
RTD has better linearity,accuracy in lower temperature,
RTD's are preferred over T/C.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / solomon
No problem.costwise T/c better.accuracywise RTD better.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / g.ramki
hi noore use RTD for good in low temp application,feed wtr
tk temp max 100deg.rtd will give good accuracy if u want to
change u ave to lay tc cable.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / arun
We use RTD in place of T/c because rtd have the greater
accracy in comparation of T/c.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / goutam
Fine Noor ,you wont face any problem but in case of accuracy rtd is better than t/c and to that you need to do the connection as for an rtd.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the meaning of GK value(fullform) in flowmeter ?
HOW DOES SPECIFIC GRAVITY AFFECT LEVEL MEASUREMENT.
what is zenier barier and what means zone 1,zone 2,and zone 3
2 Answers Bapco Bahrain Petroleum Company,
Reasons for using current as signal
What is force balance principle?
i am working in the automation company...i want to just know how actully pid control valves are tune????...
What is difference between radial vibration and axial vibration explain in detail .
NAME ANY TWO ELASTIC PRESURE SENSOR?
If hart communicator provide 4-20ma source to any transmitter during the callibration?
How can we use feedback signal frm rtd for monitoring and in dcs for controlling ,then which type of rtd is sutaible 2 , 3,4wire and why ?
We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
2 Answers National Petrochemical Company,
While preparing the graphic diagrams trend display, 3 types of trends are prepared by Yokogawa system vender. These are for process variable, manipulated variable & set point variable. Why these 3 trends are required? Explain the purpose of these 3 trends.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)