I am an electrical power engineer and arranged power system
for a data center, I installed MCB, ELCB and erthing system
TN-C-S.
But some times several ELCBs Disconnect circuits at the
same time! what may be the reason? (the ELCBs are 25A ,30mA)
Answers were Sorted based on User's Feedback
Answer / chandra
Mr. Mehdi, Do check the neutral of all circuits wether they
are connected to same ELCB group. If one neutral from one
group is connected to other group this problem will occur.
Even though all neutral is common at final point, each
neutral will have to pass through the ELCB in order to
monitor the return cuurent.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / prashant
that means tgat u wer using those 30 mA ELCB to feed ur ac/
power sockets or some other heavier load
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.p.sharma
Mr.chandra & mehndi is right and the normally mA of ELCB
used IS AS BELOW:-
1. FOR DOMESTIC = 30MA
2. FOR COMMERCIAL BUILDINGS ETC = 100MA
3. FOR INDUSTRIES = 300MA
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nageshwaran.n
Hi boss, check the connections properly.
Check for:
1. Total Load on MCB's. It should not exceed the market
rating.
2. For ELCB's, check the circuit for the leads interchange.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / mehdi
there wasn't any Falctuation in cicuits. it is strange that
if any problem occured in one circuit others may not be
failed!
I solved my problem by replacing those ELCB with 300 mA
Type!
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pillay
the choice of 30 ma is correct,
or in fact we should be able to
decide what ma rating we want
to choose where.
It could be the fault current was
quite big but fault current could
not be grounded fast enough resulting
in the current floating into other
neighbouring cct resulting in triggering
of the elcb,s.The other solution would
be checking the grounding connections from
the earth pit to upwards and also the actual
earth resistance measurements.
| Is This Answer Correct ? | 0 Yes | 0 No |
Dear Mahdi
Some Current is leakege in earth form circuit and
equepment . so your ELCB was trip.so frist check the all
circuit .
you are using TN-C-S earthing .in this common earth use
for nutral and grounding .
I suggested you for use TN-S type earthing .
| Is This Answer Correct ? | 0 Yes | 1 No |
ELCBs Disconnect circuits at the power fluctuation time or
any other reason????
| Is This Answer Correct ? | 0 Yes | 2 No |
what happens when dc supply is given to the transformer?
why transformer rating is mentioned in kva?
what is the function of turbo charger in disel generators
Is it true online ups having bypass mode if it is true then why we called ups because it is interrupting power when goes in bypass mode
What is GND Transformer?
internally connection of photvoltic module
Which theory is used in the analysis of salient pole rotor synchronous machines? Who is credited for this developement? Could the same theory be used for cylindrical rotor synchronous machines?
How I design capacitor bank for different load.7MW connected load.
Generation of voltage for each phase are same of a turbogenerator.Although the short circuit current flow when two phase of turbogenerator are shorted(where current can't flow without potential difference),why?
what kind of motors are used in the winders of coal field?and what are the various methods of it's speed control?
WHAT SHOULD BE THE MINIMUM IR VALUE FOR LV (380V) CABLES ACCORDING TO IEC/IEEE.
send me any model test paper of clerical post of state bank of india.......
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)