Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

I am an electrical power engineer and arranged power system
for a data center, I installed MCB, ELCB and erthing system
TN-C-S.
But some times several ELCBs Disconnect circuits at the
same time! what may be the reason? (the ELCBs are 25A ,30mA)

Answer Posted / pillay

the choice of 30 ma is correct,
or in fact we should be able to
decide what ma rating we want
to choose where.
It could be the fault current was
quite big but fault current could
not be grounded fast enough resulting
in the current floating into other
neighbouring cct resulting in triggering
of the elcb,s.The other solution would
be checking the grounding connections from
the earth pit to upwards and also the actual
earth resistance measurements.

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is integrated ac contact circuit

2059


The sodium vapor lamp is not glows when it is connected a distance of 5 meters above from gearbox, why ?

3651


Which motor is 3.3 or 11kV more reliable, in terms of efficeancy,maintenance, reliability.

2094


hi, i have 3x200KVA and 2 x 80KVA UPS with battery bank of 150AH 68Nos. and 100AH 204Nos., i need to install AC either ductable or PAC type, so can you help me to calculate heat load and capacity of the AC to install.

2713


What is the distance between body earthing and neutral earthing.?

4982


how to check three phase motor torque value?

2350


Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB

2716


plz send me the placement interview question and answers of whizchip(technical and apttitude)..i have an interview in next.

4979


what is per unit calculation?looking for simple and strong explanation thk u

2871


how ct burden,magnetising current,ratio and knee point voltage are related & derived

2185


what r the checklist while installing 500 kva transformer

2310


how to compute kAIC?  with formulas...

4224


How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?

4260


what are all types of cross section in AC cables?

2279


What will happen if the armature resistance is in minimum position and the field resistance is in maximum position while starting the motor

1579