what happens when a DC supply is given to AC motor?
Answers were Sorted based on User's Feedback
Answer / nd.palanivel
No rotating magnetic field is generated and hence the motor
will not rotate, instead a break is applied on the rotor for
a sort period. Depends on the magnitude of the DC supply and
the DC resistance of the coil, heat will be generated on the
coil. Coil will burn if the supply is applied continuously.
| Is This Answer Correct ? | 110 Yes | 5 No |
Earlier reply is OK, some more elaboration given below
No rotating magnetic field is generated and hence the motor
will not rotate,
No back EMF will be generated,
reactance(XL)will not come effect as frequency is "ZERO",
Rotor impedance will be remain isolated from equivalant ckt
of stator.
Only resistance of stator ckt(which is very low) will be
there. Hence stator current will be very high,Motor will
burn.
| Is This Answer Correct ? | 74 Yes | 0 No |
Answer / sunil g parit
it draws the excess current motor in not rorating due to
rorating field id not generating,it bocomes hot Or failure
of motor
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / rajan raju
WHEN DC SUPPLY IS GIVEN TO THE AC INDUCTION MOTOR THERE IS
NO PRESENCE OF ROTATING MAGNETIC FIELD SO MATOR DOES NOT
ROTATE BUT THE FIELD WINDING IS LESS RESISTIVITY SO HIGH
CURRENT WILL BE DROWN AND DUE TO THE PRESENCE OF HIGH
CURRENT MOTOR WILL MAY BE BURNED
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / pranav priyadarshi
actually when dc supply is given to ac machine there will generate const field due to which rotor won't rotate, and also stator draws large current due to which i^2*r losses is more and hence more heat is generate ,due to which machine may burnt out......
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / c.rajakumar deee.,be.,
Motor will draw more current .
A hissing sound and a dampering will occur in motor it may
damage the motor severly and results in coil burn also
| Is This Answer Correct ? | 0 Yes | 4 No |
why breather cap filled with oil?
how i calculate the syncrones generator NGR resistance .if we have a 6mw generator line voltage of generator 11kv also line current 393.3 ampere.
why three phase three wire system probably did'nt have neutral
I want to give Power supply to a house from the Feeder, Total Load of the House is 128 KW, how to calculate cable size for this load ?
what is the significance of terminal voltage and phase sequence in the operation of paralleling of two generators?
what is the value will come when megger the phase to phase ,phase to neutral ,phasae to ground ?
If the Supply voltage is increased by n times, the cross section of conducter will [increase/decrease] by ________ times ?
10 Mtr Hight of Lighting Arrestar how much area coverd??
As we know that during saturation test of CT from secondary side, the current in secondary shoots up after core saturation. How core saturation effects the secondary current?
Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.
why is the number of turns different in current and potential coils of wattmeter..?
Unbalance in voltages at motor terminals is caused by ____.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)