what is the difference between high impedance REF & REF,
same high impedance differential protection & differential
protection for Power transformer?
Answer / guest
REF protection can be implemented as High Imp or Low imp.
In high imp scheme, the CT ratios needs to be same but in
low the CT ratios may be different. Same is for the
differential protection. If the CT ratios are same the high
imp scheme can be implemneted as in busbar differential
protection.Key advantage of High imp tech is its immunity
to CT saturation . Key adv of low imp is to use CT with
different ratios for differentail / REF schemes.
Is This Answer Correct ? | 10 Yes | 0 No |
Apparent power is expressed as V * I(Conjugate). Why not in V * I ?
Why can't we parallel Voltage transformer secondary circuits?
What is SFU ?
what is x'mer ,isolation x'mer & yltra-isolation x'mer?????
What is the difference between voltages or potential difference? And what are they?
cable tray sizing & selection
iam interesting to design the control panel for 3 phase pump motors by controling single phase switches.iam plan to use fuse,contactor & relay for motor protection .how can i select the voltage & amps rating for fuse,contactor & relay plz guide me .if anybody clarify my doubt means it will more helpful for my future .
How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?
which type of effect of turbine and generator reverse power protection ?
how do you test the capacitor bank ?
for preparation of design note of 11 / 220 kV , 3 phase, 63 MVA transformer how can calculate or consider the iron losses and copper losses
How to earth the star delta connected transformers?