REF protection can be implemented as High Imp or Low imp.
In high imp scheme, the CT ratios needs to be same but in
low the CT ratios may be different. Same is for the
differential protection. If the CT ratios are same the high
imp scheme can be implemneted as in busbar differential
protection.Key advantage of High imp tech is its immunity
to CT saturation . Key adv of low imp is to use CT with
different ratios for differentail / REF schemes.
| Is This Answer Correct ? | 10 Yes | 0 No |
Post New Answer View All Answers
IF 8255 CONTROL WORD IS 94H,Tell the chip port work mode ?
how to calculate the settings for shaft ct protn in hydro generators
im working in one private compeny in gujarat. i was complet diploma electric in 2010 from gujarat technical board. now i want electric supervisor licence in gujarat but i dont't know when i apply? plz give me address of the licence dippartment office in gujarat. gandhinagar
i want to know about torque of slip ring induction motor
How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.
what is the chemical name and formula of refrigarent R-134a.
What should be setting for alarm,tripping and cooling fan on for power transformer's oil temp. and winding temp. indicator?
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
What is meant by reset level of the relay?
How phase displacement change in the over current relay coils.
i am venkat i got gre 930(verbal 270 quanta 660) and my toefl score 105..here question is why u got less score in gre ? what i supposed to tell...any chance of rejection is there...my accadamics record is very good
How can i calculate the Breaking capacity of molded case circuit breaker, is the breaking capacity of CB for Diesel generator shall be less than grid supply's breaker ?
how can we find thae value of capacitor for single phase motor. what is difference between starting capacitor and running capacitor.
WHATIS TIME CONSTANT? WHATIS ITS SIGNIFICANCE? ILLUSTRATE THROUGH EXAMLES.
What is difference between unity power factor wattmeter and upper power factor wattmeter? In short circuit test of transformer the wattmeter used is unity power factor type or upper power factor type wattmeter?