When charging a 20 MVA , 33kV/6.6kV transformer through
regulated (0-6.6 kV or 0-33 kV) source on no load , what
will be the maximum current drawn by transformer from
source and what sould be the source capacity.
Answers were Sorted based on User's Feedback
Answer / dinesh lokhande
Actually above answer is not correct as it is the full load
current.No load current is approximately 4 to 5 % of rated
full load current. hence considering the terminals (i.e HV
side or LV side) the current drawn from source will be 4 to
5 % of respective side rated current.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / satya
the charging current is about 6 times the full load current
about 2000 amps but that will be for mill seconds
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gunasekaran
for good transformer it should be 0.5%of full load current
for normal it may be upto 1%
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / pulkit
max current when on load wil be 390 amp drawn by the Hv wdg
of t/f and when on no load the transformer primary losses
occur on the basis of elctic flux principle in which when evr
the current flows in a loop,there is loss in the form of
magnetic field energy that is created arround the primary
coil.it is 1 % of the hv wdg current.
| Is This Answer Correct ? | 0 Yes | 0 No |
why HT motors are earthed only at equipment side & for it's single core cable with aluminium wire armoure using?
1 Answers Legrand, NLC Neyveli Lignite Corporation Limited,
why D.C excitation is given to sunchronous motor?
Why high voltage lines (overhead ) are called high tension lines?
What is the two pole structure?
What should be distance required in between two phase of HT cionductors in open area??????
We have Diesel generator of 200KW but load connected to it only 100KW. Pl. brief me about fuel consumption.
What is EMC filter in VVVF Drive ?
plz tell me in my que,how to connect thw electrical wirening in house?
A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of Transformer is solidily earthed) and consisting of mainly very costly and sensitive electronic equipments is giving trouble due to high voltage difference between neutral and body earth. Whether this problem can addressed by connecting neutral at the load point solidly to earth?
I need the list of Universities who have summer intake for BS degree in Electrical Engineering.?
What is the reason of polyphase induction motor tripping suddenly on high current during running at 70% laod? Motor IR , winding resistance & inductance balance. Motor no load current is balance and ok as per mgfr. data.
what is power factor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)