THE 40 MW OF POWER FOR 220 V III PHASE POWER CONNECTION
REQUIRES HOW MANY KVA POWEER REQUIREMENTS
Answers were Sorted based on User's Feedback
Answer / reshi
If we assume the power factor during motor running as 0.85.
Then the calculation will be 40MW/0.85= 47MVA.Answer.
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / riyadh
this formula u going to apply
Kw=Kva*P.f
we know P.f = 0.9 for T/f's
P.f = 0.8 for Generator
we knw power kw 40Mw
Apply to above formula Kva = kw / p.f
Kva = 40000 Kw / 0.8
Kva = 50000 kva
In Mva is 50
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / chethan
p- 40MW,v,220volts kva=?
40*1000000*4.54Amps multiply (1000=1.732*220*I,ans.4.54)
Ans. 181600 KVA
this is my knoldge ,so this is error,please tell me the
correct answer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Its 50000Kva on .8 pf and answer#3 is correct.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jayaraj
The question is wrong. 40MW load could not be fed from 220v 3 ph system. If the question is the KVA requirement 50000KVA on .8 pf. So in a distribution system 2000KVA Transformer 25 nos are required.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / v.s.narayanaswami
THE ABOVE FORMLA APPLIES FOR CONVERSION OF HP INTO KVA AND
THE CORRECT CONVERSION FACTOR IS 0.764.
THE REQUIREMENTS OF 40 HP CONNECTION CONVERTED INTO KVA
APPLYING THE FORMULA IE 1 HP = 0.764 KVA IS 40HP/0.764 IS
APPROXIMATELY IS 52 KVA.
HENCE UR CORRECT REPLY IS SOLICITED FOR ARRIVING AT THE KVA
DEMAND FOR THE ESTIMATED 40 MW OF POWER CONNECTION
REGARDS
V.S.NARAYANASWAMI
B.COM(HONS), M.COM, F.C.A
| Is This Answer Correct ? | 2 Yes | 12 No |
why phase always came one direction in 5pin socket(right hand or left hand) which direction and why..........?
I have a reading off 1.5ohms at my mem my main c/b is rated at 40/6 amps in a domestic house and i was told to change it to a b curve c/b is this ok
what iz second and fifth hormonics please explain
Whats the difference between three phase and single phase?
why the conservater tank alwes made upper side of transformer???
In Ferantti Effect Receiving end voltage is greater than sending end voltage but how it is possible. I know its all about charging current but give me some more detailed explaination?
What do you mean by phasors?
could anyone suggest project title
how to decide the ratings of the MCCB,MCB in electrification.give me the proper thumb rule or procedure.
Why converter duty transformer neutrals are not earthed...i am still not sure if this question is also correct...Please email at ranjan120482@gmail.com
How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?
what is the purpose of commutator in DC motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)