How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?..

Answer / ramesh kumar k

the size of the cable depends upon the material used in the
cable...

if u go for copper cable... the copper has got the current
carrying capacity of 2A/sq.mm continuously with out
overloading effect. so if you want for 550A,

550/2 = 225 sq.mm copper cable u have to use...

i think it is 1.2A/sq.mm for Aluminium...

550/1.2 = 458 sq.mm Aluminium cable u have to use...

like this.... the current carrying capacity is different
for different materials...

Is This Answer Correct ?    23 Yes 5 No

How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?..

Answer / dilip singh

Normally if you go with the size of cable in catalogue, you
will observe the if cable is of 400sqmm thenit carries
about 300A current and similarly for other ratings so you
can guess by size of cable selected. but it will not be
correct all the time. may it will vary by some value.

Is This Answer Correct ?    13 Yes 5 No

How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?..

Answer / u.chandarasekar

It is very vert Hard Question for me i never know the
answer.
In 28 Years exp. first time i face this kind of qus. That's
a main reason BGR Energy Terminate me.

Is This Answer Correct ?    5 Yes 1 No

How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?..

Answer / s.manikandan

we are know the formula R=Pl/A. P - resistivity of copper or
Aluminium, L - Length of wire,A - Area of wire, and We use
I=V/R formula

Is This Answer Correct ?    2 Yes 2 No

How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?..

Answer / sk

In copper cable 1sq.mm equals to 4 amps so 150sqmm*4 amps that equals to 600 amps , and we will be in safer side

Is This Answer Correct ?    0 Yes 0 No

How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?..

Answer / syed masood

t he cable size depends upon the ams rating but the cables size defined standard value the ams rating enclosed this values some values 2.5,4,6,10,......630
first you have to know full conductor size standard value
then you calculate cable size depends upon the ams by using this relation cu=2-5ams per sq.mm
al=1.2-2ams per sq.mm
4 guage for 125-150ams convert guage into mm
from kadayanallur syed masood electrical engineer
national college of engineering

Is This Answer Correct ?    0 Yes 2 No

How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?..

Answer / amit

u van not get tha exact size of cable widout catalouge

Is This Answer Correct ?    4 Yes 9 No

How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?..

Answer / binay agrawal

generally, for low rating full load current should be 3
times for aluminium cable, & 4 times for copper cable.
so, here 550/4=137.5 sq mm,
also 550/3=183.33 sq mm.
but this is for low rating, in high rating ratio is
decrease,
i.e. for copper 550/3= 183.33 sqmm
& for aluminium 550/2= 275 sq mm.

Is This Answer Correct ?    5 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

Is it possible to import & export power through the same power transformer? what will be the vector group normally for both different or same?

1 Answers  


why there is a 2 slits in three pin's earthing pin?

1 Answers  


what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?

1 Answers  


in CNC reference how to take? what kind of input give to the servo amplifier?

1 Answers  


How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set required to cater to this load?

3 Answers   Bhel, INDUS, Indus Towers,






how many parameters can integrate with fire alarm basically ?

0 Answers   Schneider,


what's ripple content in rectifier? how it formed?

1 Answers  


how did i get the competency certificate as electricle supervisor. iam completed my b.tech.but i dnt have any experince, this certificate is required for applyng ongc mangement trainees. what should i do sir please suggested me

0 Answers   ONGC,


What are the advantages of star-delta starter with induction motor?

7 Answers   Merchant Navy, Naval Academy, Samundra Institute of Maritime Studies, YMCA,


How does a tertiary winding filter harmonic(espcially 3rd one) from entering into load system?

0 Answers  


why transmission lines traveled in high voltage?

5 Answers   TATA,


What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)