How to select the Cable size for 550 Amps Load without
seeing the cable Catalogue?
Answers were Sorted based on User's Feedback
Answer / ramesh kumar k
the size of the cable depends upon the material used in the
cable...
if u go for copper cable... the copper has got the current
carrying capacity of 2A/sq.mm continuously with out
overloading effect. so if you want for 550A,
550/2 = 225 sq.mm copper cable u have to use...
i think it is 1.2A/sq.mm for Aluminium...
550/1.2 = 458 sq.mm Aluminium cable u have to use...
like this.... the current carrying capacity is different
for different materials...
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / dilip singh
Normally if you go with the size of cable in catalogue, you
will observe the if cable is of 400sqmm thenit carries
about 300A current and similarly for other ratings so you
can guess by size of cable selected. but it will not be
correct all the time. may it will vary by some value.
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / u.chandarasekar
It is very vert Hard Question for me i never know the
answer.
In 28 Years exp. first time i face this kind of qus. That's
a main reason BGR Energy Terminate me.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / s.manikandan
we are know the formula R=Pl/A. P - resistivity of copper or
Aluminium, L - Length of wire,A - Area of wire, and We use
I=V/R formula
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / sk
In copper cable 1sq.mm equals to 4 amps so 150sqmm*4 amps that equals to 600 amps , and we will be in safer side
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / syed masood
t he cable size depends upon the ams rating but the cables size defined standard value the ams rating enclosed this values some values 2.5,4,6,10,......630
first you have to know full conductor size standard value
then you calculate cable size depends upon the ams by using this relation cu=2-5ams per sq.mm
al=1.2-2ams per sq.mm
4 guage for 125-150ams convert guage into mm
from kadayanallur syed masood electrical engineer
national college of engineering
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / amit
u van not get tha exact size of cable widout catalouge
| Is This Answer Correct ? | 4 Yes | 9 No |
generally, for low rating full load current should be 3
times for aluminium cable, & 4 times for copper cable.
so, here 550/4=137.5 sq mm,
also 550/3=183.33 sq mm.
but this is for low rating, in high rating ratio is
decrease,
i.e. for copper 550/3= 183.33 sqmm
& for aluminium 550/2= 275 sq mm.
| Is This Answer Correct ? | 5 Yes | 11 No |
The objective of connecting a resistance and capacitance across gate circuit is to protect the SCR against
directional over current relay when acted & how it works
sir please send me techinical questions for junior engineer posting in bangalore railway i am diploma holder
what is the formula for calculation of sac?
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
HOW TO CALICULATE THE LEAD ACID BATTERY AH AND HOW TO FIND THE 1.2KVA UPS BACKUP @ 1000WATTS LOAD?
how to save the power in company?
If a ACB breaker is tripping and closing problem, then what will we check internal..?
first 3 men were there .again 3 came.total how much?
Load 380kva eb 415v,load amps 350.Same load dg 415v,load amps 420 what reason ?
1 Answers AVT Natural Products,
why to need a electrical earthing?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)