why power generate in 33 kv it will be step down by 11 kv .
Answers were Sorted based on User's Feedback
Answer / sridhar,psgtech
generating 33kv that will reduce the current flow
transmission line so line loss will be reduced and step
down to 11kv for distributing to consumer
| Is This Answer Correct ? | 21 Yes | 2 No |
Answer / sathish
for generation of 33kv we require large alternators thus
increase the initial investment of plant.
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / ajaya kumar.v
Normally all generating stations will generate voltage less
than 11Kv since of the isulation above 11kv, the size of
the equipment will increase. For transmission it has been
stepped up for reducing the loss in transmission &
generally the distribution system will operate on safe
voltages ie <4440V.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / vikas
Generally all the Industrial equipments are designed for 3ph
440v & domestic equip. for 1ph 230V so its easy to step down
11KV instead of 33/66KV to minimise cost of equipment as
well as losses.
Moreover for transmission of longer
range Voltage has to step up to minimise transmission losses
due to I^2R .and again has to be step down to reduce the
operating cost of equipment.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / v.chandrasekharreddy
for generation of 33kv we require large alternators thus
increase the initial investment of plant.reduse the voltage
fluctuation
| Is This Answer Correct ? | 2 Yes | 9 No |
what is the difference between HV and LV Breakers?
4 Answers GM General Motors, OEG,
why cu losses called cu losses.
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
How to select the cable and voltage drop in circuit?
What are the specifications for conducting earth leakage test as per IEC standard?
What is the effect if power factor is above 1 or unity.
What is Surge arrest? How it work?
Transformer/insulating oil tester(BDV tester)
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
what will be d.g. capacity to cater together for 14hp A.C. load & 3kw lighting load
Why 9KV surge arrester having 7.65KV of MCOV?
Diode is active or passive element?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)