When we are working on transformer(132\11KV). we are going
to isolate the transformer from both HV side and LV side.
then we are applying grounding on both side. My question is
that we required to isolate the VT which is still connected
from secondary side.?



When we are working on transformer(132\11KV). we are going to isolate the transformer from both HV..

Answer / binod

YES ,IT IS REQUIRED TO ISOLATE LINE VT IN SECONDARY
SIDE,BEACUSE BEFORE CHARGING THE TR. WE MUST MEASURE THE
INSULATION VALUE BY MEGGER
INSULATION VALUE TAKEN IN FOLLOWING MANNER
1)PH(HV)TO EARTH(EARTH CONNECTION REMOVED FROM TR. EARTH
BUSHING)
2)PH(LV)TO EARTH(IN THIS TEST THE LINE PT ISOLATED FROM THE
CIRCUIT OF LV SIDE OTHERWISE THE VALUE IS ZERO)
3)PH(PRIMARY)TO PH(SECONDARY)
4)CONTINUTY TEST BETWEEN PHASES OF LV(R Y B)&HV(RYB)

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?

0 Answers   Bhel, Jai Balaji, Rashmi Group,


in case of induction motor when overload condition or any short ckt. why stator winding burn not to be rotor winding

2 Answers  


what is PDU in transformer?? which company manufacture??

0 Answers  


why AC signals are represented by sinusoidal waveform?WHY other waveforms not used for representation

0 Answers  


WHY TRANSFORMER RATING IS MENTIONED IN KVA RATHER THAN KW

5 Answers  






We say that if voltage in a power system is increased,for a constant power the current will decrease (by P=VI). isn't this in disagreement with the ohms law(I propotional V;resistant const.).Since the resistance of transmission lines remains constant,shouldn't inc in voltage cause inc in current across the transmission line? I have read many articles across the net but still couldn't this figure this out. :( Guyz plz assist me with dis..:)..

4 Answers  


actually i can't understand what is 3dB ? and it's really not clear to me.please any one let it me be cleared.

0 Answers  


i have need all detail above basic transformer question..

0 Answers  


Name of the relay of low lub oil presuure in DG sets

0 Answers   Lineage, Sterling,


what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.

1 Answers  


I have an 15A fuse MCB that controls a night storage heater. It needs replacing and is now obsolete. Is a 16A C curve MCB the correct replacement?

2 Answers  


why alternator is used instead of dc generator and induction generator

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)