How to calculate the load loss and no load losses of the
power Transformer?
i am having the following details :
full load ct : in AMP HV :1676 ; LV:31.5 1800 KVA ;33KV/620
V for wind mill applications
Answers were Sorted based on User's Feedback
by conducting open circuit test by exciting LV winding with
rated voltage keeping HV winding open and Short circuit
test by shorting LV winding and exciting the HV winding
with reduced voltage, so that the tr. will draw a rated
current. we get no load loss. then we can predetermine the
load loss for any load or load loss is determined by
conducting back-to-back test on two identical trs.
| Is This Answer Correct ? | 12 Yes | 9 No |
Answer / ggr
The answer given by above person is some what ok, but not the reasonable answer. The question clearly mentioned the details that what they want. They need the formulae.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the In door to Out door Sub Station.
can any one suggest paper presentation topies for electrical engg?
which type of winding is used for high voltage & low current?
How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?
why do you add the load short circuit impedance when considering short circuit amperage. It seems that you should only consider supply. If you need to consider loads and you don't know what loads are to be added , what would be a good sub-transient reactance rating for the loads?
How o select the electrical fuse?.What are its characteristics.How to select the material od fuse?
what is the method to calculate the voltage drop for number of meters Example 250volts I/p at one end if the cable length is 50 meters what could be the drop?, after 100 meters how much? needs formulae.
Why is it not possible to operate a star-delta transformer in parallel with delta-delta transformer?
How to set a Zone 1 distance relay for distribution feeder?
0 Answers Schweitzer Engineering,
Whether amorphous core transformer is available in India?.If available then up to what rating of voltage and KVA?.
0 Answers DAE, Tata Chemicals,
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
For a CT the number of turns in the primary winding is.........
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)