How to calculate the load loss and no load losses of the
power Transformer?
i am having the following details :
full load ct : in AMP HV :1676 ; LV:31.5 1800 KVA ;33KV/620
V for wind mill applications
Answers were Sorted based on User's Feedback
by conducting open circuit test by exciting LV winding with
rated voltage keeping HV winding open and Short circuit
test by shorting LV winding and exciting the HV winding
with reduced voltage, so that the tr. will draw a rated
current. we get no load loss. then we can predetermine the
load loss for any load or load loss is determined by
conducting back-to-back test on two identical trs.
| Is This Answer Correct ? | 12 Yes | 9 No |
Answer / ggr
The answer given by above person is some what ok, but not the reasonable answer. The question clearly mentioned the details that what they want. They need the formulae.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is meant by fuzzy logic? what is fuzzification and defuzzification?
What is mean by staling?
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
Why there are some equipment(i.e:TV) that using 2-pin plug instead of three? What happen if there is current leakage? Are we going to get electric shock??
0 Answers College School Exams Tests,
OHMS Law is only applicable for ac or dc or both circuiT?.
what is the advantages of having in-built acvvvf (without seperate inverter in the control panel)in the drive system of elevators?
A rotor of an induction machine is delta connected. Now is there any necessacity to short the slip rings?
In UPS what does 600va reffer to?
WHY FLEXI LINKS ARE USED INBETWEEN GENERATOR TERMINAL OUTPUT & BUS DUCT CONDUCTOR.
During the troubleshooting of an inoperative shunt generator, you found the voltage to be 2+ volts; what is known from this. Is it (1). odds are the armature is good (2). odds are there is no field current flowing in field windings (3). odds are the armature is bad (4). both 1 & 2 are correct (5). both 2 & 3 are correct
Why the capacitor bank is keeping on for electricity supply and keeping it off for generator supply
if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will happen?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)