How to connect frequency meter in metering circuit?(single
phase and three phase frequency meter)phase to phase or
phase to neutral
Answers were Sorted based on User's Feedback
Answer / rvg.msceb
Frequency meter need to connect parallel with the circuit,
as its a sensing device.
there is no such 3 phase frequency meters, measuring from
one phase is more than enough.
| Is This Answer Correct ? | 73 Yes | 6 No |
Same as volt meter connection.
connected parallel with Phase & neutral.
| Is This Answer Correct ? | 38 Yes | 3 No |
Answer / anugani
Frequency meter connect in parallel like volt meter ((one prob to phase and another probe to nutral))
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / munish
frequency meter has no need of three phase.it is connected
parallel with two phases.
| Is This Answer Correct ? | 16 Yes | 4 No |
Answer / tanmay dey
Frequency meter should be connected across the line and neutral, and the voltage should as mentioned in the frequency meter(generally 120 v).
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / waleed ahmed
frequency meter also connected in parllel same as voltage mater install
| Is This Answer Correct ? | 1 Yes | 0 No |
what will happen if capacitor bank is used in generation side?
What is difference between potiential,volatge and emf
what is the voltage and ampere rating of all range of HT conductor?
How can you start-up the 40w tube lite with 230v AC/DC without using any choke/Coil?
How to calculate ht side cable of 630 kva oil cooled outdoor transformer?
What happens when two positively charged material is placed together?
HELLO EVERYONE, I RECENTLY HAVE FOUND ONE PROBLEM, I WAS TAKING NO LOAD TRIAL OF AN HT MOTOR 920 MOTOR , 1440 RPM , 6.6 KV, WITH AUTO TRANSFORMER. AT 450 V, LOAD WAS 40 AMP AND SPEED WAS 250 RPM. BUT AS WE INCREASE VOLTAGE FROM 450 TO 480V, LOAD BECOME 41 AND SPEED REDUCED TO SOME RPM . SO WHICH PHENOMENON ACTED HERE FOR REDUCING SPEED.?? AND IS IT HAPPENING ALWAYS OR IT IS RARE? I ALSO HAVE FACED SUCH PROBLEM WITH FEW LT MOTOR ALSO.
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
What is means by MacAdam Ellipse?
two transformers of the same type, using the same grade of iron and conducting material, are designed to work at same flux and current densities, but the linear dimension of one are two times of the other in all respects. The ration of kVA of the two transformer closely equal to................? options: 16, 8, 4, 2
How much current can carry the 1 sq inch super enamelled copper wire?
State the points to be considered for selecting a particular type wiring.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)