How to calculate ht side cable of 630 kva oil cooled outdoor transformer?
Answer / zahid hussain
You can simply calculate HT FLA like- MVA/Sq root of 3x HV
or my simple technic KVA/19.20, 630/19.20= 32.81A is HT side Full load current and you can use 2 times higher ratings cable....
| Is This Answer Correct ? | 0 Yes | 0 No |
What is PTZ Camera???
3 Answers Cherrytec, CSC, Honeywell, Zicom,
what are the shades for mimic diagram i.e for 3.3kv,6.6kv,11kv,22kv and 33kv? which is the IS for mimic diagram?
why we use isolation transformer?
Wht ar the reason for low voltage on consumer side?
A FIELD MAGNET IS EXITED BY AC/DC?
Cb closed condition if there is a tcs fail whether cb will trip or not
What is the control action?
R u say ,that is there is any flux in your room.
Name different types of fault and which instrument is used to measures earth,short,open cicuit fault?
6 Answers NTPC, Vijai Electricals,
The exciting current of a transformer is non sinusoidal. why?
why contactor not provided between output of VFD and motor?
Electricty is generated at around 16kV, then step up to 220kV for transmission then steped down to power transformers then DTs and then through the LT n/w it reaches the consumer end. At the consumer end 230V supply is required. So, why is electricity not generated directly at 230V and transmitted?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)