What is four quadrant metering system.
Answers were Sorted based on User's Feedback
Answer / henri groenewald
A four quadrant metering system is the metering of bi-
directional energy flow. The system must be able to meter
leading and lagging reactive energy (varh) for import
active energy (Wh) and leading and lagging reactive energy
(varh) for export active energy (Wh).
| Is This Answer Correct ? | 67 Yes | 9 No |
Answer / sath
This meter is used to measure the value in bi-directional
transmission lines.As the meter is 4 quadrant capable, it
gives forward, reverse and net readings.The meter should
deliver same accuracy of measurement irrespective to the
metered quadrant.
| Is This Answer Correct ? | 42 Yes | 9 No |
Answer / javed
It is Metering system which is used to measure Real &
Reactive Power and Energy. It is capable of measuring in
all Quadrants of Power i.e. for all possible combinations
of real & reactive Power Metering +P, -P, +Q and -Q in P-Q
(Real-Reactive) axis system
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / manish sharma
Four quadrant is a bidirectional metering system which is
capable of measuring power as below:
1. Active import while reactive import (PF lag)
2. Active import while reactive export (PF lead)
3. Active Export while reactive import (PF Lag)
4. Active export while reactive export (PF lead)
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / d.h.waiker
Four quadrant meters are those meters which can measure and
records the following parameters.
1) KW/KWH
2) KVA /KVAH
3) KVR/KVARH ( LAG )
4 ) KVR /KAVRH (LEAD )
| Is This Answer Correct ? | 28 Yes | 27 No |
If I fill the form of engineering services and I left the exam de to navoidable reasons . Will it counts my one attempt
Hello Friends, How can we recognize the CT Star Point is S1 or S2 in case of Electro Mechanical Relays and what is meant by Restraining coil in relays and what is the purpose of that.. thank you in advance..
why one side of tubelight glows after switch off ?
What is the difference between online ups and offline ups?
44 Answers Electrical Tech, GMR, Gravity India, HCL, Indus Towers, NIT, Pyramid, Techno Electric and Engineering, UBS,
i have 90kw motor.so i choose connect cable .please what is parameter checked so please give to formula
What is the difference between AC Drive and VFD?
Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing
What is the normal phase difference between the voltage and the no-load current in a transformer?
Importance of fault current in power transformers and how to monitor the same? How is it different from winding temperature?
what happend to DC shunt motor if its field winding insulation becomes slightly weak? will that motor can run on full load or not explain in detail. thanks
diffrence between windings of high tension side and low tension side of transformer
What is the clear distance between a MV panel(rear side) and wall.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)