On what basis no of earth pits are to be decided either for
transformers or for equipment?
Answers were Sorted based on User's Feedback
Ans: Transformer secondaty sholud have neutal point. This
we brought from earth. neutral point is earthed and
connected to T/F. for this we required one earh pit. and
for body earthing we should have another earh pit.
structure earthing for this another earth pit.
For an equipment we required only one earth pit for body
earthing and electrical accessories earthing( like
motors,switch gear, electronic instruments).
Is This Answer Correct ? | 23 Yes | 13 No |
There should be two distinct earth pit for TR neutral and
one for body earthing. This is as per IER. The earth
conductor crossection will depend upon the max fault
current that could flow in the system in case of a fault.
The thumb rule is, the crossecton of the earth conductor
should at least be half of one phase conductor.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / farrukh
First of all we need to know ,Why we earth the transformer
neutral,? and the answer is that ,
Transformer has three out put phases and at any time all
these phases loads are not equal, so when the load is
unbalanced on any phase, the current may flow in neutral
line,and to dissolve the current at transformer end we need
to earth the neutral. Neutral pits are used to to provide
best conductive earth.
Is This Answer Correct ? | 10 Yes | 7 No |
Answer / kartik
No of Earthing pits for a equipment depends upon components
of equipments prone to flow of fault current during
abnormal condition.Say for transformer, metal body &
neutral may carry fault current.So 2 nos pits for
transformer is required.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / meka sekhar
normally, transformer body is conned to earth mat via earth
cables. No earth pit is required for body connection.
Normally Earth pit will be provided for neutral earthing
in order to facilitate isolation.
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / sathihsa
earth pits for tr depends on kva rating and fault current
use to carry.........
Is This Answer Correct ? | 9 Yes | 17 No |
Answer / shvetang
the no of earth pits are depends upon the amount of earth
fault current that occurs during working of any equiment
Is This Answer Correct ? | 1 Yes | 12 No |
What is MS-EXCELL?
A simple Question from all.... If Voltage drops then its rated value what will be effect on a Residential load? similarly if voltage rises from its rated value then what will be effects on a load? i know if voltage drops the equipment or device draws more current then its rated what are other reasons ? thanks in advance for ur time.......
What is the importance of setting TSM & PSM?
How to calulate Locked rotor amper(LRA) for compressor type motors?
what is the difference between the electrical and electronic choke?
How to earth the star delta connected transformers?
how we can improove power factor?????????
why induction motor take more current when motor start time and this current take for 1 hours when motor is start.
How to use a insulation resistance tester on a three phase electric motor?
what would u consider to be the basic purchase order information you would need to proceed with a cable inspection assignment?
1.what is meaning of curve into a mcb. 2.what is basic reason changing of curve
What is the difference between resistance grounding system and resistance earthing system?