What is the purpose of Rotor earth fault relay and How to
test the Rotor earth fault relay in generators and What is
the procedure?.
Answer / mani_mc2006
1.one earth fault will not affect the generator more. but at
the same time if another earth fault happened it's dangerous.
2.We can test this relay by using Resistance Pot.
3.Apply the Aux supply and connect the resistance pot across
the terminals where we taken reference from the generator.
| Is This Answer Correct ? | 2 Yes | 0 No |
The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?
what is ment by doublefield revolving theory?
What is value of earth resistance required for substation and equipment earthing and what are the reference guidelines
why the tapping of transformer on ht side??????
12 Answers CTS, OPTCL, Visa Steel,
what are the standard transmision voltages in india?
What are the advantages & disadvantages of a group electrive drive?
What happens if we give ac supply to dc shunt and series motors individually
Draw a 230kv two-bus bar system showing the following. 1.Two generators (150MW) each connected through one 15.75/230KV transformers 2. 1 outgoing lines 3. Two 230/130 KV transformers 4. BUS PT's 5. CT
why capacitor is not discharged phase to body
why the transformer was not rotating like a motor?
Why is the starting current high in dc motor?
The screw thread commonly used for transmission of motion is one of the following types of threads
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)