Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate the motor winding resistance ?

Answers were Sorted based on User's Feedback



How to calculate the motor winding resistance ?..

Answer / sudheer

disconnect the motor connections and separate the wires and
check the resistance with multi meter of all winding
separately.

Is This Answer Correct ?    219 Yes 50 No

How to calculate the motor winding resistance ?..

Answer / dharmendra raninga

Please give the answer of this que.

Is This Answer Correct ?    99 Yes 55 No

How to calculate the motor winding resistance ?..

Answer / m.ramesh

how to calculate the motor winding resistance

Is This Answer Correct ?    16 Yes 6 No

How to calculate the motor winding resistance ?..

Answer / manik shinde

first apply the reted voltage & current then once we know
the v & I by voltmeter & ammeter, calculate resistance by
R=V/I.

Is This Answer Correct ?    91 Yes 83 No

How to calculate the motor winding resistance ?..

Answer / mike

you can find the resistane by using ohms law but that only
applies to a resistive load. ie.,electric heaters. for an
inductive load you'll have to call manufacture or use an
ohm meter. on a three phase motor the resistance on all
three legs should read the same or very close and on a
single phase the run and common should equal up to what
your start winding ohms are

Is This Answer Correct ?    13 Yes 5 No

How to calculate the motor winding resistance ?..

Answer / myo

The static resistance for the stator you can simply connect
the multimeter between 2 phases and arrive at the phase
resistance. Usually motors windings are delta connected. You
multimeter reading is 2/3x phase resistance.As for the rotor a
squirrel gauge motor has no rotor windings and slip ring
motors have windings connected to slip rings. In the second
case apply the same principle if you know whether the
windings are star or delta connected. For complete
determination of the equivalent equivalent circuit conduct the
no-load and blocked rotor tests.

Is This Answer Correct ?    33 Yes 27 No

How to calculate the motor winding resistance ?..

Answer / gunasekaran

first we have calculate the efficiency.
then we calculate the core loss.
loss is Isqr*R
we know load current and loss then we can calculate the wdg
resistance of the motor this is app.method not correct.
for transformer also same like that.
we can get the loss and efficiency of the motor from
manufacturer.

Is This Answer Correct ?    22 Yes 16 No

How to calculate the motor winding resistance ?..

Answer / ashour ghareeb

dc motor has four wire tow for field and other for armature
CONNECT OHMMETER,SLOWLY MOVE THE ROTOR,
IF READING IS FIXED,IT WILL BE FOR FIELD
IF NOT FIX,IT WILL BE FOR ARMATURE
SERIES-WOUND motor resistance is:
ARM.RESISTANCE
~100 &#8486;
FIELD RES.
~1 &#8486;

Is This Answer Correct ?    5 Yes 3 No

How to calculate the motor winding resistance ?..

Answer / ramesh ravichandran

in case you want to calculate induction motor winding resistance..
to get accurate value of DC resistance, firstly do block rotor test so winding of the motor get heated up at rated current..
immediately remove AC supply lines and connect DC lines across any two phase and apply 50 percent of the rated current of the IM to get the accurate DC resistance

convert the DC resistance into AC resistance by a factor of 1.2..

Is This Answer Correct ?    5 Yes 5 No

How to calculate the motor winding resistance ?..

Answer / muhammad kamran

although ohm-meter test is thorough enough but its not
complete...to find true result 1st ohm-meter reading is
taken and then in 2nd step a low voltage ac signal is
applied (using step-down transformer)normally 6:1 of
original operating voltage both voltage and current is
taken and Z-l(total impedence is taken) as unit is
performing in ac region not dc while ohm meter is dc
test.... why use this test?
not always the clear result is given by ohm meter test. a
winding may show balance state by ohm-meter but any
irregularity can be detected by AC-impedence test to be sure

Is This Answer Correct ?    14 Yes 15 No

Post New Answer

More Electrical Engineering Interview Questions

what is the formulae for selcting capacitor bank to increas pf

4 Answers  


When star connection of motor is use?

1 Answers  


hai iam arunkumar. i have applied for an section enginner in rrb. i want lat 5 years solved question papers. if u have please sedn it to arun30682@gmail.com

0 Answers   RRB,


why ac wave is sinusoidal not square or triangular wave what will be reason

1 Answers   ACPL,


What is meant by control system?

0 Answers  


a motor's measured current is 45amp,whereas the rated current is 38 amps but still it is running ,how?

5 Answers  


What will happen if the d.c. Machine is operated below rated speed?

0 Answers  


Draw the DOL starter and star delta starter drawing?

0 Answers   Danfoss,


Here iam a question with SYNCHRONIZATION PANNEL related issue, as i want to design a SYNC.pannel board iam giving the 2 nos of 1MVA Generators to sync pannel , then what wil be the out put of the sync pannel, whether it wil be one cable coems from the sync panel or two cables.. as iam using two transformers to meet my load demand, so pls clear me whether two cables comes from sync panel to connect to transformers or only one cable

3 Answers  


what is buffer resistance starter.?.What is the working principle and where it is used..?

0 Answers  


what are trouble functions of transformer?ex. prv trip,oltc,oti,wti.explain detail.

1 Answers  


what is relation between ct and pt ratio with multiplication factor of a energy meter? is there any other factor on which multification factor depend?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)