Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What are methods to avoid the inrush current at the time of
starting of power transformer ?

Answers were Sorted based on User's Feedback



What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / suresh kumar

We cannot avoid inrush current when any transformer is
switched on after a long period of shutdown. Only thing we
can do is minimising it by charging the transformer by the
lowest voltage (using tapp changers)and we can avoid
spurious tripping by inrush current by using only
transformer differential relays in which an inrush current
filter is used.

Is This Answer Correct ?    15 Yes 1 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / vinothbabu.k

BRFORE STARTING ON THE TRANSFORMER WE SHOULD SWITH OFF ALL
THE OUTGOING FEEDER FROM THE DISTRIBUTED PANEL BOARD,THEN
ON THE TRANSFORMER WITHOUT CONNECTING ANY LOAD, THEN SWITH
ON THE FEEDER ONE BY ONE,R CONNECTED LOAD.THIS THE METHOD
TO AVOID THE INRUSH CURRENT FROM THE TRANSFORMER...

Is This Answer Correct ?    13 Yes 4 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / mukhesh

their is no chanses to avoid the magnetic inrush currents
in p t/f by wn inrush curens come the t/f will doing the
vibrations to avoid vibrations steel chains are fixced

Is This Answer Correct ?    0 Yes 0 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / makku

we can reduse inrush currrent by using winding having high reactance

Is This Answer Correct ?    0 Yes 0 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / priyan

You can reduce the second harmonic by using the DELTA
connection in the CT’s but I prefer to play with the
protection relay parameters, in this case it is better to
control the differential current, there is 2 slopes for the
differential zones, try to increase the slope N01 to get
passing the inrush current.
By filtering the 2 nd harmonics, refer to relay co
ordination and set the values

Is This Answer Correct ?    1 Yes 2 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / vijay

apply a coil before applicable circuit

Is This Answer Correct ?    3 Yes 7 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / karthikeyan

Its recommended to install an CLR (Current Limiting Reactor)
befroe the Power Transformer to reduce the inrush current.

Is This Answer Correct ?    3 Yes 7 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / a.kossay

TO AVOID INRUSH CURRENT IN TRANSFORMER WE MUST USE A
VOLTAGE SENSE RELAY TO MONITOR THE VOLTAGE PEAK , SO WHEN
ITS VOLTAGE PEAK THE C.B CAN BE CLOSED AND INRUSH CURRENT
WILL BE LIMITED

Is This Answer Correct ?    1 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

How we calculate the average power factor if the one phase is lag and another one is in lead?

1 Answers   DigiTech, MCR,


why substation ratings are multiple of 11 means 11\33 kv substation

6 Answers  


Disadventage of cable-gland earthing if any ?

0 Answers  


A d.c. Shunt motor is found suitable to drive fans because they require?

0 Answers  


What is EPBX????

3 Answers   Emerson,


why dc is used in control circuit for mv & hv switchgear instead of ac

0 Answers  


I am working on a 11KV system with fault current of 40KA for 1 second. I have selected 2500MVA 11/0.433KV transformer. How can i find the impedance value for this transformer? Please help me.

2 Answers   PPL,


can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?

1 Answers   Amoli Organics,


Why the generating station rating is in KW though the rating of generators in KVA?

8 Answers   HAL,


HOW WORK HEAT PLATE EXCHANGER

0 Answers  


What are the classifications of heating element?

0 Answers   BARC,


WHAT IS DIFFERENCE BETWEEN POTENTIAL DIFFERENCE AND E.M.F?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)