how much insultion resistance 11kv cable.
Answers were Sorted based on User's Feedback
Answer / tapeshwar pandey
It should be more than 11 mega ohm as per thumb rule.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / kani
insulation resistance must be infinite otherwise leakage
current will flow ,so that insulation detoriation happen
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / murthy
Ideally in the range of 5oMohms is required for less
leakage current.2Mohms per KV of the cable at room
temperature is a thumb rule
Is This Answer Correct ? | 1 Yes | 1 No |
what precautions to be taken while desigining a LT,HT panel. Eg-LT panel PCC panel with ACB installed. HT panel VCB panel with VCB installed. & what is main diffrence betwn IP54 & IP55 construction of panel.
In Battery Charger - What is the meaning of End Cell Voltage and Float Voltage.
9 Answers FLSmidth, Focus, PSEB,
If DC supply is given to a transformer it may a) Work b)Not Work c)Give lower voltage than the rated voltage on secondary side. d)burn the winding
Why did lightening arrestor solid copper rod head is sharp on mobile tower top?
what is mcb
What are the various methods for effecive earthing in a factory in a rocky terrain, where soil resistivity is extraordinarily high? The usual method of 3 m deep earth pits is not serving the purpose.
what is the difference between ac and dc hipo test of cable?
How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.
What is partial discharge in power cable?
explain remenance . differentiate high remenance type ct & low remenance type ct
a solar energy installation utilizes a three phase bridge converter to feed energy into power system through a transformer of 400v/400v.the energy is collected in a bank of 400v battery and is connected to converter through a large filter choke of resistance 10ohms.1.the maximum current through the battrey will be.2.the kva rating of the input transformer is.
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?