Answer / sentu da
for the induction motor to act as an induction generator
we need to make the slip -ve i.e. we have to make
Nr>Ns..which is done by rotating the rotor by an external
prime mover,is S=-ve,then the S*E2=-ve and I2 =-ve, it will
induce emf in stator which will supply power to the source.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / umdl
First of all a capacitor has to be connected parallel to the stator. Then Nr> NS.. that is you have to drive motor at a speed greater that its synchronous speed( Usually Nr must be about 50 rpm grater than Ns).
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / alex
a prime mover would be installed and drive the motor above it synchronous speed, it eventually turns to an inductive generator.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / raghu .b
induction motor need prime mover to rotate the rotor at
certain speed,and slip rings to collect the power to
extranally in rotor shaft end.some other small changes
required to induction motor act as induction generator.
| Is This Answer Correct ? | 2 Yes | 4 No |
In Delta connected capcitor bank, One bank failed due to some problem. Can we connect Open delta capacitor bank to 3 phase motor. The motor voltage rating is 6.6KV. IF yes what changes will happen?
how fan speed decrease or increase by using regulator? thank you
What is the minimum distance between taransformer (say 2000 kva)and its earth pit?
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
what is the senstivity and stablity? what is different?
can I improve the furnace power factor (10 mva transformer) by adding a capacitor bank before the transformer.Does system power factor vary a lot with the furnace PF?
Brushed alternator is also called dc generator ? its true or false ?explain it ?
its Kva and Kv are same?
Impedance relay is directional relay or non directional relay?
why in india the voltage generate multiply by 11,,,like 220v,440v,11kv,33kv,66kv,220kv,
3 Answers NTPC, Servotech, Tata Power,
What is bus-bar?
how to select size of hardware for linking aluminium busbar is it depend on area of busbar or current flowing through bus bar
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)