I am having a DG set.The 415 V from Generator is step up to
460 v and then the same is used for Induction furnace.
before Step up, I am connecting LT load to my factory use.
When Induction furnace is in service from DG, when i try to
start a motor, the generator is tripped.Please tell me the
reason.
Answers were Sorted based on User's Feedback
Answer / asif.k64@hotmail.com
Also check if the motor starter is working properly and APFC
panel is off while generator starts, check the fault codes
on the breaker if you have an ACB connected in the AMF panel.
Though there could be many other reasons as well but I would
rather check these things as well.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.shanmugasundaram
Induction furnace controller is basically a rectifier cum
Inverter. Generally Rectifiers will generate Harmonics.
Suppose if the DG is not selected to accomodate this non
linear load then the sinusoidal wave form gets distorted
and will trip the DG set or other connected loads which
involves electronic circuitry. May be you can check
with an oscilloscope how the sinusoidal wave pattern
changes when Furnace is switched On. Suppose if the wave
form distortion does not happen then ther could be some
other reason
| Is This Answer Correct ? | 1 Yes | 0 No |
I Have 100Ah battery with 650VA Inverter, i WANT TO TAKE a Solar panel to charge my battery, so please suggest me,what rating of solar panel(with solar charge controller) can buy for a load of 450w for 4 hours
how many wires need to be bring to the motor if its star delta starter
In some countries it is found that an Earthing Transformer is connected at the LV sides of the Transmission and Distribution Substation Transformers.Actually what is the purpose the Earthing Transformer?
for a 400kv t/m line with 10 ampere current will corona occur?
How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???
why does connected a indutor with mnsformeretering core of current transformer ?
what are the applications of PLC?
two way ckt diagram can be drawn by how many ways? give diagram
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
what will be the maximum winding temperature of 6.6kv HT motor 450kw, Full load current 49A. 50Hz Frequency.
What is the full form of PSD & CSD ?
6 Answers NIFT, PNG Power, PSD,
how to decide cable rating? send me cable size,ampere rating data
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)