I am having a DG set.The 415 V from Generator is step up to
460 v and then the same is used for Induction furnace.
before Step up, I am connecting LT load to my factory use.
When Induction furnace is in service from DG, when i try to
start a motor, the generator is tripped.Please tell me the
reason.
Answers were Sorted based on User's Feedback
Answer / asif.k64@hotmail.com
Also check if the motor starter is working properly and APFC
panel is off while generator starts, check the fault codes
on the breaker if you have an ACB connected in the AMF panel.
Though there could be many other reasons as well but I would
rather check these things as well.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.shanmugasundaram
Induction furnace controller is basically a rectifier cum
Inverter. Generally Rectifiers will generate Harmonics.
Suppose if the DG is not selected to accomodate this non
linear load then the sinusoidal wave form gets distorted
and will trip the DG set or other connected loads which
involves electronic circuitry. May be you can check
with an oscilloscope how the sinusoidal wave pattern
changes when Furnace is switched On. Suppose if the wave
form distortion does not happen then ther could be some
other reason
| Is This Answer Correct ? | 1 Yes | 0 No |
What is effect of harmonic current (Draw by VFD) on power system/ electrical Equipments ?
Is it really necessary to have reactive power in transmission line to transfer the power from one place to other?
why C.T protection required for H.T.lines?
we hav seen in electric engine of trains only 1 wired slidng conecctn is there frm ovrhead line,howevr to complete a ckt in dc postv n negtv two conection has to b there...so where is tht negative is been connectd or where it is grounded...?
What the full form of KVARs
HOW isolation transformer works.
how do the stepper motor works.
what is the basic difference between capacitor and condenser ?
I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
We have Diesel generator of 200KW. fuel consumption is always same,even connected light load or full load. Is it right?
what is surge arresters ?........
would you please give me any idea about the BARC interview question on electrical? i have an interview on 1st july.....plz hlp me.......its urgent......
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)