I am having a DG set.The 415 V from Generator is step up to
460 v and then the same is used for Induction furnace.
before Step up, I am connecting LT load to my factory use.
When Induction furnace is in service from DG, when i try to
start a motor, the generator is tripped.Please tell me the
reason.
Answers were Sorted based on User's Feedback
Answer / asif.k64@hotmail.com
Also check if the motor starter is working properly and APFC
panel is off while generator starts, check the fault codes
on the breaker if you have an ACB connected in the AMF panel.
Though there could be many other reasons as well but I would
rather check these things as well.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.shanmugasundaram
Induction furnace controller is basically a rectifier cum
Inverter. Generally Rectifiers will generate Harmonics.
Suppose if the DG is not selected to accomodate this non
linear load then the sinusoidal wave form gets distorted
and will trip the DG set or other connected loads which
involves electronic circuitry. May be you can check
with an oscilloscope how the sinusoidal wave pattern
changes when Furnace is switched On. Suppose if the wave
form distortion does not happen then ther could be some
other reason
| Is This Answer Correct ? | 1 Yes | 0 No |
In a company has been installed an analog amperemeter, this company was suplied by generator X, there is no problem in the ampere meter, rigth now this company's supplied by generator Y then the pointer in amperemeter vibrating. What happened? Why? Thank's
Does voltage and current can be seperated?
What is the effect of using an underrated size cable to supply electrical power to a 3 phase ac electrical motor? What is the effect of using an overrated size cable for the same motor?
generally rectifying of ac tells. ac signel appear at phase and neutral with respect to frequency by -veand +cycles. but we doesn't experience shock with neutral in house hold ac??????.
what is the difference between earth leakage and earth fault?
3- What is the target from Zero Impedance, Single Phase Imp., S/C Imp. and magnetic balance tests?
What does the term power factor shows?
What is the funstion of buscoplure in LT panel? which propouse using the buscoplre
What device is use for metering current at lt consumer end..??
The synchronous speed of a motor with 6 poles and operating at 50 Hz frequency is ___.
documented proof that aluminium bus bars are better than aluminium cables
15hp,380v,31amp,3-ph submersible motor run at 250v what is The temperature rise of submersible motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)