What is meant by Reactor in power system and what are the
uses?
Answers were Sorted based on User's Feedback
Answer / jeetendra verma
when a transmission line of EHV is charged at no load, the
charging current flow between all phases will create a
capacitve effect, resulting the receiving end voltage
become more than sending end voltage.Reactors which have
very high self inductance and negligible resistance
stablize the receving end voltage.
| Is This Answer Correct ? | 115 Yes | 14 No |
Answer / naresh
reactor is inductance conected in series with transmission
feeder to minimise the magnitude of fault current.i.e.
short circuit or earth fault.
| Is This Answer Correct ? | 74 Yes | 10 No |
Answer / paritosh singha
reactor is mainly used in high voltage long transmission
line (above 200km)to compensate the ferranti effect i.e to
minimise the capacitive effect.now a line should only have a
resistance in it.but due to long transmission capacitance
comes into effect.so to nullify it we add a specific
amount(say 50 mvr)of reactor in it.
| Is This Answer Correct ? | 46 Yes | 8 No |
Reactors are mainly used to limit,the flowing of very large short circuit current during fault. it main function is to protect the plant, by limiting the amount of power that can flow into the faultier part by all other parts of the system.Eg.,Generator reactors,feeder reactors,busbar reactors,etc.
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / elaya
Reactor is a device like capacitor.which is normally
connected on high voltage swithchyard maximum 400kV in the
account of compensate reactive power on station in during
night hours (low power supply-due to industrial shut down
at night). we can classify it into two types 1.Switched
reactor 2.non swithched reactor.
simply it is power compensating device.
| Is This Answer Correct ? | 52 Yes | 35 No |
Answer / dolnarayan patel
Energy storing element in ac ckt. Used to avoid sudden
direction change of current and also to limit heavy flow of
current.
| Is This Answer Correct ? | 28 Yes | 12 No |
Answer / iddrisu habilah
Reactors are used to limit over voltages in a network
system.It is also use to absorb reactive power so that
active power can be transmitted over the network.
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / sumit sail
In order to limit the short circuit currents to a value which the circuit breakers can handle, additional reactances known as reactors.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / विशाल खरवा
Reactor is a very high inductive coil which has approx zero power losses and high reactance. Which generally used with EHV transmission lines.
Application–
1. Reactor is used to minimise the faulty current of transmission line.
2. Reactor is used to compensate the ferranti effect and capacitive effects.
3. Reactors used for connecting two lines. I.e. as a tie line connector.
4. Reactor opposes the change of faulty and dangerous current.👍👍
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / s.elangovan
reactor is a one of the current limit system in HT
Capacitor and HT transmission line.
| Is This Answer Correct ? | 10 Yes | 15 No |
should %impedance be high or low in a power transformer? if so why?
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
explain about the electrification in the Indian Railways? ie., how the power is taken and used to drive the train? explain with the block diagram??
what is the function of open delta System?
In which connection the voltage will be more , in star or delta connected motor?
types of arc quenching methodes
what r PID controllers?why they r used?what is there purpose?plz Explain in detail
what is the relation between the leading pf and supply voltage?
we have one oven for 12 zone we are installed ir lamp in oven we control load from thyrister and 0 to 5vdc so our zone no 8 getting bright in fraction of second so what we do.. Please answer
What is the difference bet ween EDO Type & MDO type ACBs, and what is the advantage EDO Type over than MDO type ACBs.
What are the three major categories of error?
11 KV distribution system where neutral is produced ?
4 Answers ciss, TATA, Tata Motors,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)