how to calibrate a control valve?
Answers were Sorted based on User's Feedback
Answer / k.thirunathan
calibration instrument required.
1.portable pneumatic calibrator
INPUT signal OUTPUT
Generate 0.2 kg/cm 0% of v/v travel
0.4 25%
0.6 50%
0.8 75%
1.0 100%
If you observe any deviation adjust accordingly.
| Is This Answer Correct ? | 137 Yes | 30 No |
Answer / deba
BY using DRUG calibrater we can easily calibrate just we
need a air line having pressure of 6kg as input of CV.
by giving 4-20mA signal through DRUG.
for example
4mA CV in close position
8mA 25%
12mA 50%
16mA 75%
20mA 100%
| Is This Answer Correct ? | 123 Yes | 21 No |
Answer / azmat
To calibrate a valve first check the input signal range if
it is 0.2 to 1.0 Kg/cm2 or different.
Calculate the span ( Difference between higher limit to
lower limit=1.0-0.2=.8 ) Now divide it in four equal parts
that is 0.2 Kg/cm2 this is 25% of the span.
Now check the valve travel like 2 inches, 3 inches or any
other value Divide it in four equal parts 25% of the travel.
Apply 25% of the span value+ 0.2= 0.4 Kg/cm2 it is 25% of
travel and apply full span value and see you get the
complete travel if you find difference adjust the spring
accordingly.
| Is This Answer Correct ? | 82 Yes | 10 No |
Answer / venkat
before do the stroke checking we have make sure the bench
calibration after that we should check 0-100% stroke
| Is This Answer Correct ? | 77 Yes | 18 No |
Answer / jayesh
If the valve is SMART now we can use a HART communicator to calibrate the control valve.Give the supply pressure according to the valve name plate then use HART communicator and give 0% 25% 50% 75% & 100% check the travelling of valve
| Is This Answer Correct ? | 52 Yes | 12 No |
Answer / shefeek salim
In Control valve Calibration,its of two types;
1.Stroke Calibration
2.I/P Converter Calibration
1.Stroke Calibration
it means for the movement (opening and Closing) measurement of stroke through the Scale,from 0 to 100 percentage of valve Closing/Opening,according to the standard air pressure supply or milli amps supply(3 to 15 psi,4 to 20 mA)
2.I/P Converter Calibrtion
It is comparatively simple one,but it can be done in two ways,
2.1 Simulate the std 4 to 20 mA as input Check the output from the I/P
2.2 Simulate the std 4 to 20 mA to the I/P converter as input and measure the Control valve stroke movement through the scale(0 to 100%)
| Is This Answer Correct ? | 25 Yes | 0 No |
Answer / c.grema@yahoo.com
first you have to now your limits if its pneumatic work
from 20 to 100kpa if current i 4 to 20ma
supply pressure,
1.bench set
2.beam alignments
3.calibration
| Is This Answer Correct ? | 30 Yes | 6 No |
what is the difference between 2 wire and 3 wire RTD- application wise,cost effectivity?
What is the difference between intrinsic instruments and ATEX instruments?
which instrument is most commonly used to observe the external features of a grasshopper's abdomen?
draw the characteristics of chebyshev filter
why we use -ve voltage in vibration monitoring system.generally we use 4 to 20 mA as output of instrument then why we use voltage in vibration
what is cold loop? difference between hot and cold loop?
I have a MRE200 amplifier for controlling a mitsubishi servo motor, I would like to know how many pulses are required to rotate the servo motor by 1 degree and what must be the pulse width
what is differences between singal acting and double action valve
1 Answers Carlo Gavazzi, Welspun,
With N nodes and B branches what will have a network ???
what is PID n give me brief info. about P&I&D.
Give me best instrumentation Books name..Ple...
Why Current(Ampere) is chosen as Fundamental Quanties not Charge(coulomb) ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)