what is the difference between star and delta connection ?
when we use each one ?what is the best ?
Answers were Sorted based on User's Feedback
Answer / infodoss
STAR Connection:
i)Supply voltage is VL/root3 but supply current
IL(line)=Iph(phase).
DELTA connection:
i)supply voltage is VL=Vph but supply current
is differ.
Both supply used in speed control of induction motor.
Transmission point of viwe delta is better.
Application point of viwe star is better.
Is This Answer Correct ? | 126 Yes | 17 No |
In continuation to Answer 1, both are having their own
importance depending up on usage. How ever where neutral is
required star system will be adopted.
Is This Answer Correct ? | 61 Yes | 16 No |
Answer / ramesh
Star Connection:
1. It is a setup where in one end of each phase is
connected together so as to form a neutral.
2. It is used for variable loadings
3. The line current = Phase current
4. The Line voltage = sqrt(3)* Phase volatge.
DELTA CONNECTION:
1. It is a setup where in one end of one phase is joined to
starting end of another end so a ring is completed.
2. It is used for balanced loads.
3. There is no neutral in here
4. Line current = sqrt(3)*phase current
5. Line voltage = phase voltage.
line volt- voltage taken from two live wire= voltage taken
from one live neural connection
Is This Answer Correct ? | 27 Yes | 6 No |
Answer / zahid khan
star is only used intial to because the supply voltage is
VL/root3 and due to high starting torque of induction
motor,'star delta circut used above 20kw.
Is This Answer Correct ? | 29 Yes | 13 No |
Answer / kb shrinivas
IN STAR CONNECTION THE LINE CURRENT EQUAL TO THE PHASE
CURRENT AND LINE VOLTAGE GREATER THAN PHASE VOLTAGE ,
VPH=VL/ROOT3 AND IN DELTA CONNECTION THE LINE CURRENT
GREATER THAN PHASE CURRENT , IL=IPH X ROOT3 AND LINE
VOLTAGE IS EQUAL TO PHASE VOLTAGE AND FINALLY BOTH
CONNECTIONS ARE VERY USEFUL IN THE 3 PHASE SYSTEM.
Is This Answer Correct ? | 20 Yes | 6 No |
Answer / s k singh
For transmission, delta connection is suitable while for
distribution system, star connection is sutable because
nuetral is available in star connection.
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / rajkumar voorugonda
star connection is used when we need nuetral ,
d connection can be used to decrease the circulating
current in the system
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / nardos negash
4 transmition and 4 the motor at rated speed delta is
better b/c the current in delta is small/line at its
voltage than in Y so it saves the winding and the
insulation from over heating.
Is This Answer Correct ? | 18 Yes | 10 No |
Answer / rahul
In star connection neutarl is already provided, so when we need neutral, we shold use star connection.
delta connection is used to reduce the effect of circulating current in the circuit.
Is This Answer Correct ? | 14 Yes | 6 No |
Answer / glen
delta is prefered becoz it torque and power is greater as
compared to star connection
star is only used initial to becoz of the Supply voltage is
VL/root3 thus preventing drop in the line
Is This Answer Correct ? | 32 Yes | 26 No |
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
what is the long transmission lines
hoe we can exlain the effect of caoacitor in fans????????
what is resver in electrical enginnering with answer
how to test an MCB
how to convert the KVAR to microfarad??????????????????
Battery is a voltage source? give one example of current source and why?
what is the meaning of TPN
how to calculate the starting current of a motor? gopal
What is the differance between 2 dc motors of armature voltage 660 v and 440 v?
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
I am apply the AAI. So i want electrical sample question paper in technical with answer my id is vijayjobsmart@gmail.com
0 Answers AAI Airports Authority Of India,