Answer / bharat
In DC motors, Voltage equation is V=Eb-IaRa
V = Terminal voltage
Eb = Back emf in Motor
Ia = Armature current
Ra = Aramture resistance
At starting, Eb is zero. Therefore, V=IaRa
Ia = V/Ra where Ra is very less like 0.01ohm.
i.e, Ia will become enoromously increased.
Ref. Electrical Technology Auth : BL Theraja, Vol-I & II.
| Is This Answer Correct ? | 37 Yes | 3 No |
Answer / rama krishna
The simplest way to start a three-phase induction motor is
to connect its terminals to the line. In an induction motor,
the magnitude of the induced EMF in the rotor circuit is
proportional to the stator field and the slip speed (the
difference between synchronous and rotor speeds) of the
motor, and the rotor current depends on this EMF. When the
motor is started, the slip speed is equal to the synchronous
speed, as the rotor speed is zero (slip equal to 1), so the
induced EMF in the rotor is large. As a result, a very high
current flows through the rotor. This is similar to a
transformer with the secondary coil short circuited, which
causes the primary coil to draw a high current from the
mains. When an induction motor starts DOL, a very high
current is drawn by the stator, on the order of 5 to 9 times
the full load current. This high current can, in some
motors, damage the windings; in addition, because it causes
heavy line voltage drop, other appliances connected to the
same line may be affected by the voltage fluctuation. To
avoid such effects, several other strategies are employed
for starting motors.
| Is This Answer Correct ? | 4 Yes | 10 No |
Isolation transformer primary to sec turns ratio?
What will be the average KVA rating of Auto Transformer for 75kw 415V , 3phase induction motor
what is vcb & working principal
How to calculate % Impedence?
what is the function of impulse relay
draw the restricted earth fault protection circuit install on power transformer and identify its parameters and draw C/C curve of it
What it the purpose of parallel phasing transfomers??
How to select the different contactors ( starter combination) for different AC motors? what about fuse cappacity 4 different motors too?
what is difference b/w CFL and Ordinary lamps? which one is useful for power saving?
I have motor 1500 HP and , 4160 V , 60 HZ , then i need the rating of transformer which can feed that motor ??
how to decrese the PH value of liquid resistance?
which starter is used for synchronous motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)