A 6.6 KV motor breaker is try to Drack OUT by me while the
motor running. What will Happened?
a, will Trip.
b,Drack Out lever will not access
c, will get shock
d, noting will happened
Answers were Sorted based on User's Feedback
Answer / vinayak
For 6.6 KV Motor's VCB haves inbuilt interlock that if you
try to rack out VCB it will trip VCB and naturally trip
Motors. IS/IEC will not permit omit this intelock.
In Case if interlock not working, It will produce arching
and Noise at point of disconnection of contact.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shahid mukhtar
there is a mechanical lock which inhibits breaker to
rackout in case of breaker close. so you cannot rackout
braker in close position.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sri rama murthy
electrical flash can take place as it happened in my
industry
Is This Answer Correct ? | 1 Yes | 1 No |
In convertor can we use rectifier thyristor in place of invertor thyristor with explain.
generally the electrical equipments not to be operated at leading power factor, why?
Can we use BS 6651 and BS EN 62305 standards for computer room lightning ptotection in substation?
what is derated current of power cable & what is formule to find derated current?
how is efficincy of the transformer is predermined
Before given the connection to Alternator (pre- commissioning) which tests we will conduct
How does zener phenomenon differ from avalanche breakdown?
What is diversity factor and how to calculate it
2 Answers Al Faraa, Amul, Pentagon, Sobha Developers,
what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm
what is smartµ grid technology?under coal gassification?
wath is skin effect?
for any load, what happen if we use the cable rating above its normal rating