A 6.6 KV motor breaker is try to Drack OUT by me while the
motor running. What will Happened?
a, will Trip.
b,Drack Out lever will not access
c, will get shock
d, noting will happened
Answers were Sorted based on User's Feedback
Answer / vinayak
For 6.6 KV Motor's VCB haves inbuilt interlock that if you
try to rack out VCB it will trip VCB and naturally trip
Motors. IS/IEC will not permit omit this intelock.
In Case if interlock not working, It will produce arching
and Noise at point of disconnection of contact.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shahid mukhtar
there is a mechanical lock which inhibits breaker to
rackout in case of breaker close. so you cannot rackout
braker in close position.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sri rama murthy
electrical flash can take place as it happened in my
industry
| Is This Answer Correct ? | 1 Yes | 1 No |
what is the basis for selection of Protection CT class ? How anyone can decide whether to go for 5P10 or 5P20 ?
What is the use of lag compensator?
v=I*R, i.e V is directly proportional to I. now P=V*I. so V=P/I. thus v is inversely proportional to I. so what is the correct one? If both are correct than for which kind of condition this 2 differ
what does mean ct knee voltage and burden
Explain briefly about current , voltage and power
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
1 Answers Eprosys Engineering Consultants,
what is MULTIPLYING FACTOR in substations??
calculate external resistance values to add to the rotor of a slip ring induction motor. STATOR- 415 V, 3 phase delta, 1100 A, 50 Hz, 1490 rpm, pf 0,86 ROTOR - 660 V, 590 A, 50 Hz. STATOR current at each steps STEP1-600A,STEP2- 800A,STEP3-1000A,STEP4-1100A.
WHY LINK NOT A FUSE IN AC CIRCUIT
if installing the transformer why put the sprit the stone ?
What makes the difference between 50Hz supply and 60Hz supply which one is economical and how can you support your answer...........?
2 Answers Fertichem, Kuwait Oil Company,
WHAT IS THE SPECIFICATIONS CONSIDERED DURING DESIGN FOR THE OVER CURRENT RELAY?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)