Describe the method of Plate Earthing.
Plate earthing provids using copper plate (450mm x 450mm x
6mm). The area of the copper plate is high causing high
earthing value (Low resistance).
Instaling Method: The copper plate at the depth of 2 Mtr or
3 Mtr. The centre support provides using 40mm GI pipes,
funnel in top.The two numbers of 25mm x 3 mm copper flat
stamped from top of the GI pipe to copper plate to improve
the earth value. The salt, charcole to improve the
conductivity.
The materials using for plate earthing are as below:
1) Meshed Funnel
2) 40 x 300 x 6 mm copper earth pad
3) 25 x 3 Cu strip
4) Copper Rivit
5) 450 x 450 x 3 mm Cu plate
6) 8x25 mm bolt and nut with washer
7) 6x75 mm bolt and nut with washer
8) 40 mm GI pipe - 2.8 mtrs
9) 25mm dia x 200 mm length GI pipe with double end threaded
10) 40mm to 25 mm GI reducer
11) 1" Check nut(6mm thick)
12) Charcoal
13) Salt
14) 450 x 450 mm heavy duty SFRC chamber cover with frame
ersaravananp@gmail.com
Saravanan.P
| Is This Answer Correct ? | 6 Yes | 1 No |
what does mean ct knee voltage and burden
why knee point voltage should be high in Ct for differential protection
pls send me some of the solved question booklet of Junior Engineer -2 (ELE) in RRB
What is cathode ray oscilloscope (cro)?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
what is humming noise and wha is the reason to develop humming noise in a mv pannel ?
a room heater is connected in serise with a 100w bulb.if the 100w bulb is replaced by a 40w bulb then the output of the heater is increase/decrease/remain same?
9 Answers College School Exams Tests,
why vaccum circuit breakers are preferred over m.o.c.b
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
what is the difference between STAR and DELTA connection and application wise how it can be utilizedd ???
What is Creepage distance?
america 60hz electric supply is used; but india it is 50hz; why? and if we use 60 hz supply what changeg has to be done or all the equipment has to be thrown which has rating of 50hz frequincy
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)