why we can choose induction machine in wind mill? why can`t
use synchronous machine?
Answers were Sorted based on User's Feedback
Answer / manish meena
The reason is that syn. motor is mainly designed for
constant speed operation,as wind is not blowing with
constant speed,so we can not use syn motor.
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / just some guy
It all depends on the connection to the grid. Synchronous
machines can be used as well, but they have to be decoupled
by power electronics to adapt the frequencies of the wind
voltage and current to the grid voltage. Induction machines
are very reliable and there is less maintenance expected. So
the answer would be: We could use the syn. machine, but the
distribution system would have to be built on different
considerations, which might be more costly.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sameer
first we know that
synchronous motor is
not self starting
motor so it reqired dc
exitation to the rotor
and this problem is
not in i.m so if we
consider to connect
motor to wind mill
than we need to power
produce not the use
otherwise it decrase
efficiency and also
synchronous motor is
complicated
construction then i.m
so
| Is This Answer Correct ? | 0 Yes | 0 No |
what is green house effect?
why the star delta motors burn out frequently
What is super thermal power plant? and how it will differ from normal thermal power plant
HOW TO CALCULATE EARTHING SIZING?
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
If the neutral wire go pass through the core balance current transformer? If yes then why? and no then why?
we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440v?
How to model two generators into a single generator ? Eg. two generators connected to a bus, would like to model it as a single generator connected to a bus.
how many wires need to be bring to the motor if its star delta starter
how to minimize earth resistance upto 2Ω, if the resistance is 6 Ω ?
what is the permissible bend in the LT& HT CABLES.
what is looping circuit in electrical lighting circuits?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)