Answer / raju
Relays are 3 types
1. Mechanical relay
2. electromechanical relay
3. numerical relay
RELAY WILL SENCE THE FAULT CURRENT THROUGH CURRENT
TRANSFORMER AND IT WILL GIVE A COMMAND/ SIGNAL TO TRIPPING
COIL WHICH WILL TRIP THE BREAKER.
Is This Answer Correct ? | 22 Yes | 0 No |
Answer / anand shukla
a relay is a sensing device ,which sense the fault and give
signal to the circuit breaker.
relay are many types which is is used in different
conditions.
1- electromagnetic relay
2- thermal overload relay
3-directional & nondirectiobal relay.
4- distance relay
5-mho relay
6-trip circuit supervision relay
7- master trip relay.
in realy some types of contacts are fitted
like no and nc which is interchange when current exceed a
preset value it means when relay operated.
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / simpal
Relay is basically a switchgear which senses the fault
occuring in the system and give signal to circuit brekar 2
remove the healthy part from the faulty part
Is This Answer Correct ? | 12 Yes | 7 No |
Answer / chowndaryaa sehar
Relay is the device which will sense and isolate the fault
by giving a signal to circuit breaker with help of a
controller chip.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / ramanharikrishnan
Relays are working with sensation of fault while
occuring in system.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sindhuja
Relay works with with inputs of CURRENT... VOLTAGE..
BASICALLY- CURRENT OPERATED AND VOLTAGE OPERATED.
Relay has the element.
if the element sense the I or V .. which crosses the set
valve .. then it operates.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nagesh
Relay is switch which can be operated by rated power supply
at the rated current...Relay consists of NO and NC contact
which operates depending on the Coil
Ex ---NO contact will become Close when relay is activated
------NC contact will open when relay is energised
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / bhumi
Relay is one kind of electro mechanical device with is
intended to sence the fault(the situation which is opposite
to its normal operation & as well as the function of the
relay for which it has been made)& to give command to the
circuit breaker immediately to isolate the faulty part from
the healthy portion to save the entire system.
Is This Answer Correct ? | 1 Yes | 1 No |
What is the meaning of Insulation H for transformers????
What is the difference between automatic & semi-automatic star-delta starters?
what is the difference b/w neutral and earth?what is the need of earthing and what are the different methods for earthing?
how to calculate restraing current and operating current for differential protection if 20 mva transformer is OLTC 33 kv/11 kv ? and what should be the type and ratio of CT?
How damper winding in synchronous motor suppress Hunting?
What is third harmonic?what is the effect of it?
Write a note on RC operational amplifier as integrator
upto how many load can v connect to stabilizer which is used for tv
why Power transmssion voltages are as 11kV,33kV,66kV,220kV and so on only?
if the magnetic lines can pass through a vaccuum area
what happen if i connect DYn11 and DYn1 vector group transformer in parrallel?other things are same like votage ration,x/r ratiob etc...
Why transmission line carryiny high voltage and low current?
3 Answers apspdcl, Universal Power Controls,