How we detect the leakage current of 11 KV H.T. motors and
waht is the maximim limit?
Answers were Sorted based on User's Feedback
Answer / jeetendra verma
leakage current causes due to detoration of insulation it
can be determine by partial discharge methord
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / prabhu gnanasekaran
There are two issuse excisting 1.Leakage current2.return
current. Return current is nothing but the it is a small
amout of current that flows in the neutral when the circuit
is not closed. These neutral current can be senced by RCD
(Recidual current devises). Wheareas the leakage current is
one when your cable is shorted or any open circuit to the
ground which can be senced by CORE BLANCE CURRENT
TRANSFORMERS. When there is no leakage current then the
current in all the 3 core will be same. If any leakage
current excits then the current will not be same.
Is This Answer Correct ? | 11 Yes | 6 No |
3ph motor running with unequal kw and different pf what are the reasons
What is class X ct? What rare its uses?
how do u calculate CT rating for 10 mva transformer
What are the test involved in DG auto synchronizing panel before in manufacturing place before dispatch.
WHY TRANSFORMER RATING IS MENTIONED IN KVA RATHER THAN KW
why electron not flow in open loop,how they know path is open ?
how to calculate the battery AH
What should be the height of basement according to NBCC code?
From the point of view of accuracy in the Measurement of Electrical energy should we select a potential transformer or a capacitor voltage transformers?.Kindly support your reply with reason and justification.
In dc ckt. 24v or 110v, which one is more efficient and why?
What is meant by unilitrel device?plz tell about h-parametrs
what is the thumb rule or formula for cable size and current ratings