How we detect the leakage current of 11 KV H.T. motors and
waht is the maximim limit?
Answers were Sorted based on User's Feedback
Answer / jeetendra verma
leakage current causes due to detoration of insulation it
can be determine by partial discharge methord
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / prabhu gnanasekaran
There are two issuse excisting 1.Leakage current2.return
current. Return current is nothing but the it is a small
amout of current that flows in the neutral when the circuit
is not closed. These neutral current can be senced by RCD
(Recidual current devises). Wheareas the leakage current is
one when your cable is shorted or any open circuit to the
ground which can be senced by CORE BLANCE CURRENT
TRANSFORMERS. When there is no leakage current then the
current in all the 3 core will be same. If any leakage
current excits then the current will not be same.
| Is This Answer Correct ? | 11 Yes | 6 No |
we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards
What is the difference b/w chock and ballast?
in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel ?
how to select the no. of brushes in a lap winding?
Don't you have similar question banks related to Oral Certification Examination conducted by Mercantile Marine Departments / Directorate of Shipping, Ministry of Shipping for Electro Technical Officer?
0 Answers Bernhard Schulte Shipmanagement,
what is brushless generator.How does work it..??
what is the difference between surge protection capacitor and surge arrestor
A 230 v dc series motor is connected to 230 V ac supply, then
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
What is GIS (Gas Insulated Switchgear)
what is dry and wet frequency withstand voltage? why & where it is used??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)