if generator is running in iso mode parrallel with grid and
suddenly grid breaker off what will happen?
Answers were Sorted based on User's Feedback
Answer / blake australia
If generator is running in ISOC mode (opposed to base
loading) and the grid connection is lost the generator will
try to pick up the load on the connected network. If the
load is too big then the generator will trip. If the load
isn't the generator will continue to run as before. ISOC
mode means that the generator is running in its own
frequency control, so if it looses the grid frequency it
can still run based on its own frequency.
If the generator was running in base load and the breaker
trips the generator will have no frequency reference.
Usually they are configured to change themselves back into
isoc when grid reference is lost but you should check if
unsure.
Is This Answer Correct ? | 17 Yes | 1 No |
Answer / vincent omwikha
depending with load supplied, the generator will continue
running if it can sustain the load, but it will trip
immediately if the load is to big for it
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pg
Generator can not run in Iso Syn mode while running
parralel with Grid.
If it is runnin parallel with grig in Iso Syn mode it will
trip in Overload or reverse power.Because in iso mode
Generator run at constant frequency and grid frequency vary
so it may overload or trip on reverse power.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / mahmud
many reasons-
1.ROCOF settings.
2.O/U voltage
3. O/U Frequency
etc.
Is This Answer Correct ? | 2 Yes | 2 No |
documented proof that aluminium bus bars are better than aluminium cables
What is the difference between earthing & neutral.
How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?
how a single machine can act as both motor and generator? and give explanation interms of connections?
What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?
What are the advantages of speed control using thyrister?
Need help. 3 phase system. Neutral line arced and melted upon connection of connector with 3 phase power. Why would that happen?
IN CONTROL SYSTEMS Y WE NEED TO KNOW THE STABILITY OF THE SYSTEM?WHAT IS ITS PRACTICAL USE?
why there is a temperature rise at different metal to metal contact at cable lug??suppose cable is aluminium and the lug is copper,than why the temperature rise takes place??
What is the function of UV coil ACB?
In a circuit a capacitor (paper capacitor ) was burned due to over voltage in this case can we replace that type cappacitor with other tye capacitor ?
how can we change the phase angle b/w two phase?