Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


if generator is running in iso mode parrallel with grid and
suddenly grid breaker off what will happen?

Answers were Sorted based on User's Feedback



if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / blake australia

If generator is running in ISOC mode (opposed to base
loading) and the grid connection is lost the generator will
try to pick up the load on the connected network. If the
load is too big then the generator will trip. If the load
isn't the generator will continue to run as before. ISOC
mode means that the generator is running in its own
frequency control, so if it looses the grid frequency it
can still run based on its own frequency.

If the generator was running in base load and the breaker
trips the generator will have no frequency reference.
Usually they are configured to change themselves back into
isoc when grid reference is lost but you should check if
unsure.

Is This Answer Correct ?    17 Yes 1 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / vincent omwikha

depending with load supplied, the generator will continue
running if it can sustain the load, but it will trip
immediately if the load is to big for it

Is This Answer Correct ?    5 Yes 1 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / mahmud

black out may happen.

Is This Answer Correct ?    7 Yes 4 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / anil

why?

Is This Answer Correct ?    2 Yes 1 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / pg

Generator can not run in Iso Syn mode while running
parralel with Grid.
If it is runnin parallel with grig in Iso Syn mode it will
trip in Overload or reverse power.Because in iso mode
Generator run at constant frequency and grid frequency vary
so it may overload or trip on reverse power.

Is This Answer Correct ?    3 Yes 2 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / mahmud

many reasons-
1.ROCOF settings.
2.O/U voltage
3. O/U Frequency
etc.

Is This Answer Correct ?    2 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

How we can change the direction of rotation of Induction motor? Prove it using graphical methods.

2 Answers  


why dc motor is called constant flux motor?

1 Answers  


What should do when induction motor take more load in single phase ?

1 Answers  


1.what is meaing of ups,and used in softwares and sud stations,and main partes in ups. 2.main partes of the Disel Genarator. 3.main partes of the chiller and safty equipments.

2 Answers  


what will happen if 11KV is given to 1.5 square mm cable connected with constant load of 10A ?what will be the condition of cable after injecting the voltage?

1 Answers  


how many voltage or current enough to kill a person?

12 Answers  


resistivity of copper

1 Answers  


how we can decide that what value of ht line will come to any commercial building? (ans except According to the building load)

0 Answers  


area control error

0 Answers  


What are the limitations of Kirchoff's laws?

0 Answers  


whata is battery charger ?how many cells connected for 110v?

1 Answers   Essar,


what is power system.........?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)