Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why Delta Star Transformers are used for Lighting Loads.

Answers were Sorted based on User's Feedback



Why Delta Star Transformers are used for Lighting Loads...

Answer / t eswara rao

For lighting loads, neutral conductor is must and hence the
secondary must be star winding. and this lighting load is
always unbalanced in all three phases. To minimize the
current unbalance in the primary we use delta winding in the
primary. So delta / star transformer is used for lighting loads.

Is This Answer Correct ?    81 Yes 5 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / naheru arun

i think there are mainly two resone
1. in a big sub station or in company power supply is used
for plant load (which is generally use only 3 phase neutral
is not used)this supply also used for plant lighting which
is require neutral to obtain this neutral we use Delta Star
transformer which is also called isolation transformer
2. Delta star transformer is used to isolated secondary
side earth fault (which is common in lighting circuit) from
primary side.

Is This Answer Correct ?    7 Yes 0 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / guest

delta-star transformers are used for lighting loads
because in delta side primary side the voltages fed are in
phase (R-Y-B) and thus on the secondary side the star
connection aims at equal currents in all the phases in case
of 3 phase thus equal current flows and thus the lighting
intensity is not disturbed for the lighting loads.

Is This Answer Correct ?    23 Yes 20 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / p krishna teja

in delta connection there is no common point ( i:e no
netural) for lighting we need netural line for
maintaining voltage difference. so star connection is need
for lighting .

on delta connection 3 phase we can only get 415 volts as
there is no netural line we cant use individual phase .
But in stare connection 3 phase ther is flexibility of
using individual phases with common netural 230 volts.

Is This Answer Correct ?    7 Yes 5 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / ravi

Bcoz to obtain Phase to Netural Voltage..

Is This Answer Correct ?    8 Yes 7 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / b.b.barah nalco

I agree with Mr. P Krishna Teja but one thing is there, to minimize the fault current secondary winding should be star connection and minimize the watt loss.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

WHAT SHOULD BE THE RATING OF generator required to run a pump motor of 45 Kw.

1 Answers   Jauss Polymers,


How many types of electric motors are there?

0 Answers  


Why does the rotor rotate?

0 Answers   Elin, OPTCL,


why 400Hz is used for aircraft systems ?

14 Answers   Cabin Crew, Jet Airways,


work of choke in florocent tube circuit ?

0 Answers   Bhel,


What are the Steps for Testing of 20MVA (make:-CGL) Transformer? How many Test we have to do?

2 Answers   BSL,


Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing

0 Answers  


Define closed loop control system.

0 Answers  


need help, please can someone tell me how can i calculate the main breaker and branches breakers to distribution panels (MDB) depending on the load ampere .. i really need it but can't find any site >>

3 Answers  


what is the use of the circle diagram

2 Answers  


I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.

1 Answers  


How to calculate or formula to calculate rhe power in 2 phase system ??

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)