Answer / t eswara rao
For lighting loads, neutral conductor is must and hence the
secondary must be star winding. and this lighting load is
always unbalanced in all three phases. To minimize the
current unbalance in the primary we use delta winding in the
primary. So delta / star transformer is used for lighting loads.
| Is This Answer Correct ? | 81 Yes | 5 No |
i think there are mainly two resone
1. in a big sub station or in company power supply is used
for plant load (which is generally use only 3 phase neutral
is not used)this supply also used for plant lighting which
is require neutral to obtain this neutral we use Delta Star
transformer which is also called isolation transformer
2. Delta star transformer is used to isolated secondary
side earth fault (which is common in lighting circuit) from
primary side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / guest
delta-star transformers are used for lighting loads
because in delta side primary side the voltages fed are in
phase (R-Y-B) and thus on the secondary side the star
connection aims at equal currents in all the phases in case
of 3 phase thus equal current flows and thus the lighting
intensity is not disturbed for the lighting loads.
| Is This Answer Correct ? | 23 Yes | 20 No |
Answer / p krishna teja
in delta connection there is no common point ( i:e no
netural) for lighting we need netural line for
maintaining voltage difference. so star connection is need
for lighting .
on delta connection 3 phase we can only get 415 volts as
there is no netural line we cant use individual phase .
But in stare connection 3 phase ther is flexibility of
using individual phases with common netural 230 volts.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / b.b.barah nalco
I agree with Mr. P Krishna Teja but one thing is there, to minimize the fault current secondary winding should be star connection and minimize the watt loss.
| Is This Answer Correct ? | 1 Yes | 2 No |
In 3 phase induction motor 1hp current rating is 1.5 amps constant ? is correct or not ?
What is the difference between MCCB & MOCB?
what will be the min and max voltage flow from neutral to earth?
Hi i want to know that in generation station what we are generate either voltage or current
What is the current carrying capacity of 0SWG,3SWG,10 & 12 SWG solid bare overhead copper conductors?
How to test the vector group of a Yd11 transformer? what are the relations to be checked between various vectors to confirm this vector group?
What is bus-bar?
WHAT IS BASICS TO SELECTION OF 11 kv Trasformer, send any calculation sheet for selection of transformer
why does same amount of current flow in the circuit inspite of any number of resistances in the circuit?
Zone of protection and tripping scheme of arc protection relay.
what will be the energy loss =? Voltage drop = ? Conductor resistance at 20 degree C = ? Temprature convertion Factor at 50 degree c = ? on ACSR DOG Condutor at following data. distance = 4.8 kM Load = 2980 kWh Size of Conductor = 6/ 0.186 Volt = 11 kV.
1 Answers Pakistan Atomic Energy Commission PAEC,
what is different the DOL Starter and Star Delta STARTER
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)