Why Delta Star Transformers are used for Lighting Loads.
Answers were Sorted based on User's Feedback
Answer / t eswara rao
For lighting loads, neutral conductor is must and hence the
secondary must be star winding. and this lighting load is
always unbalanced in all three phases. To minimize the
current unbalance in the primary we use delta winding in the
primary. So delta / star transformer is used for lighting loads.
| Is This Answer Correct ? | 81 Yes | 5 No |
i think there are mainly two resone
1. in a big sub station or in company power supply is used
for plant load (which is generally use only 3 phase neutral
is not used)this supply also used for plant lighting which
is require neutral to obtain this neutral we use Delta Star
transformer which is also called isolation transformer
2. Delta star transformer is used to isolated secondary
side earth fault (which is common in lighting circuit) from
primary side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / guest
delta-star transformers are used for lighting loads
because in delta side primary side the voltages fed are in
phase (R-Y-B) and thus on the secondary side the star
connection aims at equal currents in all the phases in case
of 3 phase thus equal current flows and thus the lighting
intensity is not disturbed for the lighting loads.
| Is This Answer Correct ? | 23 Yes | 20 No |
Answer / p krishna teja
in delta connection there is no common point ( i:e no
netural) for lighting we need netural line for
maintaining voltage difference. so star connection is need
for lighting .
on delta connection 3 phase we can only get 415 volts as
there is no netural line we cant use individual phase .
But in stare connection 3 phase ther is flexibility of
using individual phases with common netural 230 volts.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / b.b.barah nalco
I agree with Mr. P Krishna Teja but one thing is there, to minimize the fault current secondary winding should be star connection and minimize the watt loss.
| Is This Answer Correct ? | 1 Yes | 2 No |
please send the last 5 years {{{JUNIOR ENGINEER - ELECTICAL, ELECTRONICS RRB CHENNAI and secundrabad}}} TECHNICAL question papers TO MY EMAIL ID dinesh100701@gmail.com
if earthing is not connected to computers any problem ?
What is the functaion of IGBT in UPS system?
What is polar plot?
pls tell us AC plant are how do work and parts name with picture
What are marginally stable systems?
can we use CBCT in neutral of solidly grounded transformer? in place of three phases we can pass only one phase which decreases the size of CBCT?
Why TAP changer provided in primary side of HT transformer ? and why not in secondary?
Can anyone tell the proper diagram of star delta starter????
why threre are two parallel lines in transformer's symbol?
why there is a fault occurs, if a phase wire touches ground.. and the fault not occurs when we connect a bulb between phase and ground..??
any body know about lighting arrestor. how to determine the height of lighting rod from top of bulding and how many area it cover.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)