Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why Delta Star Transformers are used for Lighting Loads.

Answers were Sorted based on User's Feedback



Why Delta Star Transformers are used for Lighting Loads...

Answer / t eswara rao

For lighting loads, neutral conductor is must and hence the
secondary must be star winding. and this lighting load is
always unbalanced in all three phases. To minimize the
current unbalance in the primary we use delta winding in the
primary. So delta / star transformer is used for lighting loads.

Is This Answer Correct ?    81 Yes 5 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / naheru arun

i think there are mainly two resone
1. in a big sub station or in company power supply is used
for plant load (which is generally use only 3 phase neutral
is not used)this supply also used for plant lighting which
is require neutral to obtain this neutral we use Delta Star
transformer which is also called isolation transformer
2. Delta star transformer is used to isolated secondary
side earth fault (which is common in lighting circuit) from
primary side.

Is This Answer Correct ?    7 Yes 0 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / guest

delta-star transformers are used for lighting loads
because in delta side primary side the voltages fed are in
phase (R-Y-B) and thus on the secondary side the star
connection aims at equal currents in all the phases in case
of 3 phase thus equal current flows and thus the lighting
intensity is not disturbed for the lighting loads.

Is This Answer Correct ?    23 Yes 20 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / p krishna teja

in delta connection there is no common point ( i:e no
netural) for lighting we need netural line for
maintaining voltage difference. so star connection is need
for lighting .

on delta connection 3 phase we can only get 415 volts as
there is no netural line we cant use individual phase .
But in stare connection 3 phase ther is flexibility of
using individual phases with common netural 230 volts.

Is This Answer Correct ?    7 Yes 5 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / ravi

Bcoz to obtain Phase to Netural Voltage..

Is This Answer Correct ?    8 Yes 7 No

Why Delta Star Transformers are used for Lighting Loads...

Answer / b.b.barah nalco

I agree with Mr. P Krishna Teja but one thing is there, to minimize the fault current secondary winding should be star connection and minimize the watt loss.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between isolators and electrical circuit breakers? What is bus-bar?

0 Answers  


what is mean by harmonics?Type of harmonics?

6 Answers  


what is the purpose of high speed earth switch in gas insulated substat

0 Answers   ABB,


the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?

0 Answers  


Why you want to join non technical field when you are an engineer?

0 Answers  


the rating of fuse wire i always expressed in what?

3 Answers  


Show formula which gives full load current 4.8 amps of a 3 HP motor and 27 amps of a 20 HP motor having 3 phase 460 volts, 0.8 Pf.

2 Answers  


How can we get electric power from lighting ?

3 Answers   TATA,


how can we phase identification in a distribution line,how we recognise that which phase is coming for a house hold connection.help me............

0 Answers  


it says in neutral wire current flows under normal condition, but when we put tester it wont glow, why?

7 Answers   HCL,


can we run AC & DC cables in same tray

1 Answers   Aurobindo,


if we have 320KVA Genset kindly advice how much load we can put it.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)