Answer / t eswara rao
For lighting loads, neutral conductor is must and hence the
secondary must be star winding. and this lighting load is
always unbalanced in all three phases. To minimize the
current unbalance in the primary we use delta winding in the
primary. So delta / star transformer is used for lighting loads.
| Is This Answer Correct ? | 81 Yes | 5 No |
i think there are mainly two resone
1. in a big sub station or in company power supply is used
for plant load (which is generally use only 3 phase neutral
is not used)this supply also used for plant lighting which
is require neutral to obtain this neutral we use Delta Star
transformer which is also called isolation transformer
2. Delta star transformer is used to isolated secondary
side earth fault (which is common in lighting circuit) from
primary side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / guest
delta-star transformers are used for lighting loads
because in delta side primary side the voltages fed are in
phase (R-Y-B) and thus on the secondary side the star
connection aims at equal currents in all the phases in case
of 3 phase thus equal current flows and thus the lighting
intensity is not disturbed for the lighting loads.
| Is This Answer Correct ? | 23 Yes | 20 No |
Answer / p krishna teja
in delta connection there is no common point ( i:e no
netural) for lighting we need netural line for
maintaining voltage difference. so star connection is need
for lighting .
on delta connection 3 phase we can only get 415 volts as
there is no netural line we cant use individual phase .
But in stare connection 3 phase ther is flexibility of
using individual phases with common netural 230 volts.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / b.b.barah nalco
I agree with Mr. P Krishna Teja but one thing is there, to minimize the fault current secondary winding should be star connection and minimize the watt loss.
| Is This Answer Correct ? | 1 Yes | 2 No |
WHAT SHOULD BE THE RATING OF generator required to run a pump motor of 45 Kw.
How many types of electric motors are there?
Why does the rotor rotate?
why 400Hz is used for aircraft systems ?
14 Answers Cabin Crew, Jet Airways,
work of choke in florocent tube circuit ?
What are the Steps for Testing of 20MVA (make:-CGL) Transformer? How many Test we have to do?
Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing
Define closed loop control system.
need help, please can someone tell me how can i calculate the main breaker and branches breakers to distribution panels (MDB) depending on the load ampere .. i really need it but can't find any site >>
what is the use of the circle diagram
I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.
How to calculate or formula to calculate rhe power in 2 phase system ??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)