WE Know that different supply voltage of solenoid valve like 24,110,220 etc..how we check the solenoid supply is 24v or 220 NOTE: No specification at device.
Answers were Sorted based on User's Feedback
Answer / ayaz
MR Carl Ellis
Solenoid in workshop not in service and no specification on the solenoid how to know we usage solenoid
for example field supply for solenoid is 24 v dc and no new in warehouse and how to check and use older solenoid without specification
| Is This Answer Correct ? | 0 Yes | 1 No |
1) Put a voltmeter on the solenoid terminals and see what the control signal supply voltage is. It could be AC or DC.
2) Go back to the control signal source and trace the wires until it becomes apparent what the control signal voltage is.
3) Dig out the electrical drawings and see what control signal the circuit was designed for.
4) Measuring winding resistance is dicey (not terribly reliable) because the wattage ratings on solenoid coils covers a range of about 3:1, so the difference between a DC coil and an AC coil, or between a 6 or 9 watt coil is overlapped by different wattage coils for different services.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 3 No |
what is radar type level transmitters and its basic principle and how to calibrate it
WHAT IS THE Differance b/w on/off & pid control valve?
Difine flashing , Cavitaion & Noise? how to minimize these effects
calculate the rane of level use of this values, h=3 meter density=0.9 , whats the rang?
How to calculate the flow rate in Vortex flow meter?What is K factor?Can you give me an example calculation to understand the same as better?
In control valve proximity inductive sensor is taken as digital feedback for full open and full close.Normally its volts 24v when the sensor acts the feed back voltage 14v so that our relay not indicating in plc panel . kindly give the solution.
What are the processes Variables?
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
What is DCS?
We have ZR22G-100-S-A-E-T-T--E-A/CV/F1 Model Zirconia Oxygen analyser which is Yokogawa make. I kept the analyser in Flue gas path at Air pre heater area. My plant is 7.5MW Biomass power plant. For a particular fuel, Coconut Husk which contains Sodium and Potassium chlorides iam not getting proper reading, Analyser output always Zero. I calibrated the analyser and it is OK. For Other fuels like Wood chips, Cholam waste, DOB, Groundnutshells, Ply wood waste and all iam getting actual percentage of Oxygen. What is the main reason behind this draw back?
why we use -ve voltage in vibration monitoring system.generally we use 4 to 20 mA as output of instrument then why we use voltage in vibration
Reasons for using current as signal
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)