CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE
IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND
TAKING OUTPUT FROM PRIMARY?
Answers were Sorted based on User's Feedback
Answer / premgin
See transformer mainly used for step up purpose are of the
detal-star connection,the advantage is that in the seconary
for step up the insulation req is lessa s the voltage is
57.7 of actual vaue in secondary.So consdier ur question
now? is it advantageous.Transformer designs are done not
merely on load,but the winding
insulation,oil,insulation,cooling,etc are also important.
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / ashokreddyreguri
The given t/f is 415 v/200 v(h.v/l.v).
If the supply is given to 415 v side and o/p is taken from
200v side then it is step down t/f.
If the supply is given to 200 v side and o/p is taken from
415 v side then it is step up t/f.
We can use the same t/f tor step up and step down operations
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sabale.dnyaneshwar@gmail.com
again it is depend upon type of your winding.
practically it is possibble.
also agree with 9th ans. & 13th ans.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nazheer
the process of applying voltage from secondary to primary is
know as back charging.... yes. it can be used as a step up
transformers........ in power plants GT will be tested
through back charging........
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / student
For the same KVA rating we can use the transformer with
corresponding increase or decrease in the voltage and load
current.Eventhough theoretically it is possible no
manufacturers prefer because of the practical difficulties
as explained in Ans # 2 and 3.
So combining Ans # 2,3 and 9 we can say its not practically
advisable to use the transformers in such a way.
Is This Answer Correct ? | 1 Yes | 2 No |
Hello all,
That really a good discussion what about the vector
displacement. Whether it has to be taken into account or
not.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / m.vishwanath
this method can be followed only for testing of transformer
without any doubt but practically cannot be as explained in
ans 2
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / padmanabh thakur
in previous answer I mistyped that dielectric strength is
depend on pd sorry for that,actually rapturing of insulator
is depend on Pd.insulation used in low tension side is small
dielectric stength and this insulation will break down when
we will used high pd across low tension side
but in theory point of view we can used
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / padmanabh thakur
Actually when transformer is manufactured winding
insulation have major role.That is the number of
turn,insulation strength
and many other factor does remain same in both
winding.dielectric strength mainly depend upon
voltage(p.d).As potential difference is increased
,electrostatic stress on insulator is increase and at
certain voltage insulation rapture.Dielectrc strength of
insulator used in high tension side is high compare to low
tension side.
When low tension side of transformer is connected with high
voltage then there is chance of insulation failure.Because
dielectrc strength of low tension side is small as compare
to high tension side.
Theoretically it is possible.
Is This Answer Correct ? | 5 Yes | 10 No |
Answer / vinothbhabu.k
its not possible,the while designing the the transformer we
should calculate the capacity of load,according to the
load the insulation level oil level be designed,so its not
possible one..
Is This Answer Correct ? | 1 Yes | 12 No |
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
how open delta PT works & what is its construction?
In Plumbing services What are accessories we consider for a bathroom?
What is C2-M2-E2 class in circuit breaker. why and where it is to be used in circuit breaker
What is the formula of frequency ?
When should I use earth leakage circuit breaker for incomer and when should I use it for each feeder seperately?
why the admittance matrix or y bus matrix of a large network is called sparse matrix?
what happends when an isolater is operated on on-load
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
pls tell what are doing the three phase motor star and delta connetion with circuit diagram and control wiring .
What will be the capcity of 3 phase DG set require for 25 KVA single phase lighting load?
what the reson to use phase shift( angle) like (dyn11,Dd5 or Dy0)are usedin power and transsmison line