what is full form of lv and mv? 2.while we connect
capacitor to generator what will cause for it?
Answers were Sorted based on User's Feedback
Answer / rajkumar r
LV-LOW VOLTAGE
MV-MEDIAM VOLTAGE
IF WE CONNECT CAPACITOR TO GENERATOR ADDITIONAL LOAD COME
UNDER DG MEAN TIME PF ALSO S IMPROVED
Is This Answer Correct ? | 32 Yes | 4 No |
Answer / ibrahim s
LV - lOW VOLTAGE
MV - MEDIUM VOLTAGE
Cpacitor is used to correct the power factor(bring power
factor value close to unity, thus minimising wasted energy
and improving the efficiency.
It is not always necessary to reach a power factor of 1. A
cost effective solution can be achieved by increasing your
power factor to greater than 0.95
Is This Answer Correct ? | 16 Yes | 4 No |
Answer / siddu
connecting capacitor bank across the generator will disturb
the stability of generator operation because of uncntrol
reactive power components.normally this is not advisiable
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / mahesh sonawane
Full form of
lv - Low Voltage
mv - Meadium Voltage.
If we connect capacitor to generator it may act as
additional load on the generator or it may boost up the
generator volatage to higher level for which generator
shuold have some protection and it can be used to improved
power factor as it injects the reactive power required by
inductive load or for the energy saving purpose.
Is This Answer Correct ? | 13 Yes | 5 No |
can any one explain about when EB supply failed then how the load will transfer onto DG's step by step.
what is differents between static stablizer and servo stablizer
Why different values of B’s (magnetic flux density) are chosen for DC machines and Induction Motors?
why the transformer has no starter
In hydro plant,generally we install vertical hydro generators..why dont we recommend horizontal one??
Why LT cables are not sized based on short circuit capacity.
we have one pumping station and 4.6 MW 7 no.s synchronous motors.so there is no required HT capacitor to improve power factor.But we have two no.s of 25 Mva power transformer connect to distribute the power for motors connect with 220 kv line.So i have required the HT capacitor to improve power factor at HT side i mean power transformer bus side.So please suggest how much HT capacitor banks required for same.
Why the ceiling fan has three blades, why not two,four or five?
i am using auto transformer for starting of induction motor to provide reduse voltages...but the principle of a tansformer according to definition"which transform energy to on circuit to another circuit with constant power and constant frequency". so if i am using reduse voltage then current obsely hige because power is same.but we use auto transfarmer for starting of induction motor to give low current.but here according to definition we are giving hige current.
how to test reverse power trip?
why current flows from +ve to -ve terminal
there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.
5 Answers Construction, wbsedcl,