In the diesel generator if there is an AVR (auto voltage
regulator) gone faulty, in this condition is there any way
to generate the voltage from the alternator? I need a brief
explanation can you please help somebody
Answer / sheikh
in any type of generators if AVR has become failed
then not possible to generate the voltage, because excitation
is comulsory to megnetized the alternator field winding
in case of AVR faliuer exitation also must be failed becaus
AVR is supplied the exitation volage either no load condition
or on load condition AVR also incrase and decrease the
exitation voltage and current as per demand of load.
Is This Answer Correct ? | 5 Yes | 0 No |
Grounding. Dear all at one of my site we checked the amps at the earthing cable to the alternator it was found 125 to 130 A. at the neutal cable in same machine found 146A. in the same plant checked the earthing current on other alternator it was 52A, and neutral 116 A. we are facing problems with our controller and the card was damaged once. can that neutral/GND current be a reason? as there is common grounding for the Alternator,Brkr panel,Transformer?
I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?
Why armature rheostat is kept in maximum position?
Why use only DC supply to charge batteries why not AC Supply??
If a earth leakage circuit breaker trips is it possible to tell which house circuit breaker (I have four) is the faulty circuit?
Is it advantages of having star-delta vfd than normal star vfd , if yes why?
working principle of UPS
how to calculate lighting for a room
How will you justify IR value and Charging voltage of any motor,transformer and Cables.......???? . . . . . . . . Plz tell me any body Baljeet Singh, engineer_89@refiff.com
what is difference between 3.5 core and 4 core cable
WHAT IS MEANING OF VECTOR GROUP FOR TRANSFORMER
what is the meaning of spur line?