What are the difference between C-Curve and D-Curve for
MCB's.
Answers were Sorted based on User's Feedback
Answer / sean foley
answer 11 is pretty much right.
A basic rule of thumb is
B - beyond normal lengths (for very long cables)
C - common (normal) installation
D - Demand on start-up (high initial "rush" current on
motors / heat pumps)
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / venkatesh s.r
"C" curve is used only for lighting because of Starting &
runnig current is same in that circuits
"D" curve is used in electronis circuit like
computer.Because of it will be with stand high armonics &
initial rash current.
| Is This Answer Correct ? | 8 Yes | 79 No |
Answer / g.venkat reddy
MCB are classified as
B,C,D,K curve type
intant..trip current,
C....2-5 times the rated current.(motors,Ltg,inductive
loads)
D....10-20 times the rated current.
(Drives,computers&capacitors)
| Is This Answer Correct ? | 15 Yes | 109 No |
Answer / bcd
The difference between B, C and is the following.
B is the second letter of alphabet.
C is the 3-th letter of alphabet.
D is the 4-th letter of alphabet.
Thank you for your attention. ... (Take it easy).
| Is This Answer Correct ? | 39 Yes | 178 No |
What is meant by Load Encroachment in OHL Feeder Protection?
why we are caling 440 volt 3 phase supply instead of 660 volt 3 phase supply? because each phase as a voltage of 220 volt. if anybody know the answer for my question please send it to my mail id. thank you.
3 Answers College School Exams Tests, Jindal Steel and Power, JIOL, NEC,
What is switch gear? How it is work ?
1 Answers AbaQulusi Municipality, Lupin,
What is meant by transformer, why it should be used, with out that equipment what happens if we transformed the supply?
How many electrones need to flow in one second to equivalent to one Ampere.
what is the difference between UPS & Inverter
What is Anemometer used to measure?
A 3-PHASE TRANSFORMER IS USED TO STEP-DOWN THE VOLTAGE OF A 3-PHASE, 11KV FEEDER LINE. PER-PHASE TURNS RATIO IS 12.FOR A PRIMARY LINE CURRENT OF 20A, CALCULATE THE SECOUNDRY LINE VOLTAGE, LINE CURRENT AND OUTPUT KVA FOR FOLLOWING.A)STAR- DELTA.B)DELTA-DELTA.
hoe to test voltage restrained overcurrent relay?
Acually generator neutral is earthed,if suppose cable from neutral is brokened under theearth ,what will happen.
What are the three major categories of error?
Dear sir, my knowledge about cable size determination is limited. Though I read examples I could not calculate the Cable size required for electric driven pump 40 KW, 380 Volt, 50 HZ, 50 meter from transformer and it is three phase star delta starting. Please help as there is no one in my surroundings to help.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)