What are the difference between C-Curve and D-Curve for
MCB's.
Answers were Sorted based on User's Feedback
Answer / sean foley
answer 11 is pretty much right.
A basic rule of thumb is
B - beyond normal lengths (for very long cables)
C - common (normal) installation
D - Demand on start-up (high initial "rush" current on
motors / heat pumps)
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / venkatesh s.r
"C" curve is used only for lighting because of Starting &
runnig current is same in that circuits
"D" curve is used in electronis circuit like
computer.Because of it will be with stand high armonics &
initial rash current.
| Is This Answer Correct ? | 8 Yes | 79 No |
Answer / g.venkat reddy
MCB are classified as
B,C,D,K curve type
intant..trip current,
C....2-5 times the rated current.(motors,Ltg,inductive
loads)
D....10-20 times the rated current.
(Drives,computers&capacitors)
| Is This Answer Correct ? | 15 Yes | 109 No |
Answer / bcd
The difference between B, C and is the following.
B is the second letter of alphabet.
C is the 3-th letter of alphabet.
D is the 4-th letter of alphabet.
Thank you for your attention. ... (Take it easy).
| Is This Answer Correct ? | 39 Yes | 178 No |
how many earthing required for ups, what should be the earth voltages
What is the principal of motor?
What Is HO factor in power selection
i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection
After taking shutdown of 11kv feeder, if you see 5kv by phasing stick in the cable side, is it possible to close earth switch in cable.
In 2500kva transformer how much is the withstand High voltage power frequency between primary to secondary and earth? And secondary to primary and earth?
voltmeter kya hota hy ?
is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.
why ct is testing using dc.. y cant we use AC insted of dc on POLARITY TEST.
why vaccum circuit breakers are preferred over m.o.c.b
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.
what can be the causes of capacitor start motor having a higher current that its actual
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)