how to reduce power loss when the tranmission under long
distance?
Answers were Sorted based on User's Feedback
Answer / minal
we use high voltage transmission under long distance to
reduce power loss.
Is This Answer Correct ? | 15 Yes | 0 No |
Answer / sandy
Increase the transmission voltage. Naturally the current
will go down.
Is This Answer Correct ? | 16 Yes | 4 No |
Answer / ravi prakash
POWER LOSS IS ISQUARE R.WHEN WE HAVE TO REDUCE POWER LOSS IN
LONG TRANSMISSION LINE ,WE HAVE TO REDUCE THE CURRENT I. FOR
THE SAME LOAD POWER LOSS CAN BE REDUCED BY INCREASING THE
POWER FACTOR.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / mani
We have to increse the transmission voltage and current can
be reduced so losses will be less
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / daher
increase the transmission line cross section to reduces the
resistance .
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / comil83
To reduce power loss in HV line u have to reduce current in
trasmission line so voltage will remain as high as
pssible.so u can overcomes from more voltage dropp.For
reducing current in line u have to apply the formula R =
L/A.Where L leanth of conductor and A = circumfanc of
conductor.In ur case lenth of con. is long.so to reduce R u
have to increace A(Thick cable).If R is reduced then losses
of voltage will less but it will also increase your capital
cost of cable transmission.Other way is you can us step up
X'mer at some distance u can improve ur voltage trnsmission
but in this cas also capital cost of ur extra x"mer will
more and also some loss in X"mer is also there.
So u have to select a methode as per ur industrial
aplication.
Is This Answer Correct ? | 6 Yes | 0 No |
to reduce power loss in transmission lines
1)the voltage will have to be increased .but there will be
limitaions for this also
2) the distace between conductors should be as long as
possible to reduce inductance in case of ac transmission
3) highly conducting meterials based on the economy have to
be taken such as aluminium
4)power factor should be more .the more the power factor is
the less the current is .so losses are reduced
5)hvdc transmission is also another option
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / anil
By reducing current because 'cu' loss depends on current
Is This Answer Correct ? | 6 Yes | 3 No |
if we have a power factor 0.99 and we add a capacitive bank with it then what happen?
WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >
Please give me the formula stating relation between AC & Dc.
where used impendence relay?
pls tel me the electric train traction motors name plate details like rpm,torue,voltage,amps,watts..ect..
Write the force balance equation of ideal spring element.
As per the Anchor capstan motor specification, full load current is 200A. starting current is 1750 A and acceleration time is less than 8 seconds. Please guide for selection of cable size.
A 3-PHASE TRANSFORMER IS USED TO STEP-DOWN THE VOLTAGE OF A 3-PHASE, 11KV FEEDER LINE. PER-PHASE TURNS RATIO IS 12.FOR A PRIMARY LINE CURRENT OF 20A, CALCULATE THE SECOUNDRY LINE VOLTAGE, LINE CURRENT AND OUTPUT KVA FOR FOLLOWING.A)STAR- DELTA.B)DELTA-DELTA.
why we multiply 11 in High Electric supply?(eg.11KV, 33Kv, 330Kv etc.)
what is wave traps and why it is been used in switchyards?
what about SAP/MRP regarding manufacturing of electric motors and all drives?
Where the Dry type tranformers are used.