How to conduct Magnetic Balance Test, Measurement of
Excitation Current (both on HV- and LV-side) and vector
group on a 1000 KVA distribution transformer. There is a
neutral on HV side.
for magnetic balance test apply the 415 v volt to R phase
then measure Y phase voltage it must be 60 to 80 % of i/p
voltage and B phase should measure around 40 to 20 % of i/p
volatge and when voltage applied to Y phase R & B phase
should read 40 to 60 % of i/p reading. For voltage applied
to B pahse reading should be reverse of first case.
and for measuring excitaation current just give 415 V to
either side H.V or L.V but H.V side prefer and measure
current with clamp meter of all phases.
and for vector group just short the R phase of H.V with r
Phase of L.V
measure voltage as
1R-1Y =
1Y-1B =
1B-1R =
1Y-2y =
1Y-2b =
1B-2b =
1B-2y =
then e.g Dyn11
these condition to fullfill
1Y-2y = 1Y-2b
1B-2y > 1B-2b
Is This Answer Correct ? | 7 Yes | 1 No |
what is meant by MCB and MCCB? and what its full form?
how much kn lightning arrestor is used in 11kv line
how terminal voltage increases when load is capacitive (leading pf load)? (explain practically what is happening, not using phasor diagram
distribution is maximum done by a)radial b)network c) parallel d)b & c
I have a drawing of a wound rotor induction motor for a crane. This crane motor has 5 forward speeds & 5 reverse speed implemented of course with different amount of resistance for each speed setting selected. What has got me scratching around is the fact that 8 of the 10 speed selections switch in uneven (unbalanced) amounts of resistances on each of the 3 connections to the motor's rotor.Can this be possible? I would have assumed this would produce unbalanced rotor currents and therefore vibration in the motor. I would greatly appreciate anyone's comments on this. Many thanks, Confused.
Does the motor power displayed on the Motor name plate is the mechnical power motor delivers or it is consumed power from the system?
What type of input will the OLTC indicator will accept or what type of output the OLTC will produce to monitor it's position at remote location.
why synchronous motor is not self starting
can you send me the placement papers of electrical engg. from companis like NTPC,DRDO,IOCL,HPCL,BPCL etc.?If,plz send as soon as possible.Thanks.
How to calculate VCB rating for 33KV ,25 MW Power line?
What Different of Ht Side VCB & SF6
How to findout raw or ups power? its not indicated in socket,