How to conduct Magnetic Balance Test, Measurement of
Excitation Current (both on HV- and LV-side) and vector
group on a 1000 KVA distribution transformer. There is a
neutral on HV side.
for magnetic balance test apply the 415 v volt to R phase
then measure Y phase voltage it must be 60 to 80 % of i/p
voltage and B phase should measure around 40 to 20 % of i/p
volatge and when voltage applied to Y phase R & B phase
should read 40 to 60 % of i/p reading. For voltage applied
to B pahse reading should be reverse of first case.
and for measuring excitaation current just give 415 V to
either side H.V or L.V but H.V side prefer and measure
current with clamp meter of all phases.
and for vector group just short the R phase of H.V with r
Phase of L.V
measure voltage as
1R-1Y =
1Y-1B =
1B-1R =
1Y-2y =
1Y-2b =
1B-2b =
1B-2y =
then e.g Dyn11
these condition to fullfill
1Y-2y = 1Y-2b
1B-2y > 1B-2b
| Is This Answer Correct ? | 7 Yes | 1 No |
what is is the potential diffrence between two phase ?
I have 3KVA Libert GTX2 UPS. I need to calculate the back up time with some load. How to calculate the Back time. I need the expert guide
what is the use of capacitor in online ups?
why the secondary current transformer cannot left open
CBCT selection
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
How can find thermal state value in relay for calculate thermal overload.
how instantanious short circuit current is calculated ? its formula.
keeping in view of parallel operation which of the 3 phase transformer connection are possible? a)delta-delta to delta-star b) delta-delta to star-delta c) star-star to delta-delta d) delta-star to star-delta
Where the Dry type tranformers are used.
following are the questions asked in interviews: 1) Considering the short circuit fault, which switchgear is preferable, SFU OR MCCB? Which operates faster? whicg one is popular in Indian Market and why? 2)Define SCPD. What is type2 coodination? 3)Why the contactor rating is higher for the fuseless selection than for fuse selection? whether the ratinf of SFU or MCCB remains the same in both the cases? 4)If the HP rating is known then can you calculate the ratings of L.V Switchgear(SFU/MCCB, contactor, OLR) without using the selection chart?
how to test power transformer.YNd11
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)