IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO
11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE
LOADED ABOVE THE SOURCE GENERATOR RATING?
Answers were Sorted based on User's Feedback
No. Tranformer is for only stepping up the voltage, not the
power which should not be allowed to rise above the
capacity of the generator
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / hareesh k.s.
No.
The source generator rating is 100X1000VA/415X1.73=133A
therefore the maximum load that can bear by the source of
power supply is 133A.
but the tranformer maximum output
current=500KVA/11KVX1.73=26A.
therfore the maximum load rating that can bear by the
trasformer is 26A.
ie.500KVA,11KV transformer can loaded upto only 26A.
but the maximum source KVA is 100KVA
therefore the maximum output load rating of
tranformer=100KVA/1.173X11KV=5.25A
so the conclusion is in this case the tranformer can be
loaded upto 5.25A(11KV).
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ben
firstly a 100kVA 3-phase WYE generator will only produce 100kVA of power, this will also more than likely be rated at 0.8 power factor meaning the true power you will receive will only be 80kW.
if you are using a 500kVA, 415V/11000V step-up transformer you will probably find that the 100kVA generator is not large enough to saturate the transformers magnetisation current. i would have to say you need either a larger generator or a smaller transformer to suit your site needs.
In answer to your questions: No it can not.
Is This Answer Correct ? | 0 Yes | 0 No |
Why 5kv megger used to megger 6.6kv motor or 33kv transformer why not 500v?
What do you mean by distributed winding in alternators? how exactly is 3 phase power generated?
What Is Sampling?
0 Answers Mahatma Gandhi University,
what's the meaning of the negative going half cycle in the circuit containing a bulb and a switch in series with a input ac source. i mean what happens in the -ve cycle. the dir. of current changes or any other thing. if dir. changes then why we use fuse in only phase wire.
Why is it preferred to use a wattmeter(s) to measure power in three phase systems rather than using a combination of other instruments e.g. voltmeters, ammeters etc?
I have a 25kVA three phase transformer on our property. Will this transformer be large enough to run a large home with swimming pool, spa, 2 off full size reverse cycle air conditioners to service a 100 square house (10,000 square feet or 930 square metres)and the general power consumption of this house without upgrading to a 63kVA transformer.
what is the difference between line & phase current in star delta connection motor?
how can check the resistance of battery contact?
why dc is used in control circuits for MV & LV switchgeras instead of ac
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases slip A does not alter B decreases C increases D none of above
why we can't use more then 50 hz in india ? Is it possible ?
which type of stability limit is higher,steady state or transient? why?